S7lite ladder program
May 2009
Bacolod City
39
Hi guys, am a bit of a beginner, trying to learn plc programming ...in step 7 lite software, can you please give me an example of a ladder program...(analog input and analog output), thanks
Hi Ivo,
Thanks for the help, but the FC105 my way of understanding is for the analog input scaling, how would I write the program to output the analog input proportionately to the say for example control valve?
Thank you Ivo.... Have already tested the program and it work well.(4-20mA input equals 4-20mA output), but I cannot monitor the out in FC106 (PQW256 output) in my laptop or in the HMI. I have assigned the PQW256 as an integer and it doesn't show anything unlike in the FC105 out (PIW256)-which can be monitored. Please help.
Normally PQW 256 is not assigned to the PIQ (proces image outputs)so you can not monitor it straightforward inside a VAT.
Try this:
L PQW256
T MW 100
and look at MW100 inside a VAT.
You cannot use the instruction L PQW256
If you want to monitor a PQW then transfer it to a MW first and then to the PQW address, you can then monitor the MW
e.g.
I would write my own FC as a wrapper for FC106 and include an extra output for monitoring purposes:
Code:
FUNCTION FC 1106 : WORD
TITLE =
VERSION : 0.1
VAR_INPUT
  IN : REAL ;
  HI_LIM : REAL ;
  LO_LIM : REAL ;
  BIPOLAR : BOOL ;
END_VAR
VAR_OUTPUT
  OUT : INT ;
  MONITORED_OUT : INT ;
END_VAR
VAR_TEMP
  iData : INT ;
END_VAR
BEGIN
NETWORK
TITLE =
      CALL fc106 (
           IN                       := #IN,
           HI_LIM                   := #HI_LIM,
           LO_LIM                   := #LO_LIM,
           BIPOLAR                  := #BIPOLAR,
           RET_VAL                  := #RET_VAL,
           OUT                      := #iData);
      L     #iData;
      T     #OUT;
      T     #MONITORED_OUT;
      SET   ;
      SAVE  ;
END_FUNCTION
L D[AR2,P#0.0]:
Thanks, indeed you are correct for the same reasons as I wanted to point out. Only I forgot that even this is impossible to do. Show me that testing/controling is always a part of the solution.
Edit: and now it hits me: I intended to use the method in post #7.