Why?but i want to stop and reboot the other remote cpu.
S7 315-2PN/DP does not support SFB20.
Why?
If you have network access to the remote CPU, you have to go online using STEP 7 (V5.x or TIA Portal) to STOP and RUN the CPU.
Why?
If you have network access to the remote CPU, you have to go online using STEP 7 (V5.x or TIA Portal) to STOP and RUN the CPU.
In the specifications of the S7-31x and S7-31xC CPUs are listed what SFBs and SFCs are supported, not what is not supported. SFB 20 is not listed as supported.
Also, in your other thread on the same topic (!), you wrote yourself that SFB 20 was not on the CPU.
There is a software redundancy solution for S7-300.I want to make a redundant system. Running plc to stop the other
6ES7862-0AC01-0YA0
SIMATIC S7, SW redundancy V1.2 single license for 1 installation R-software (for two CPUs), SW and documentation on CD, Class A, 5 languages(de,en,fr,es,it) Executable in Win95/98/ME/ Windows NT/2000 Prof., Reference HW: SIMATIC S7-300/400 CPU 315 and higher
There is a software redundancy solution for S7-300.
But it is not a good solution.
Siemens themselves once told me "do not use it".
Yes, i wrote. but when i check it SFB14 is also not in the CPU. But now it works.
I think there are people who run and use it in some forums.
SFB14 and SFB15 are only supported on S7-400.I am currently doing data transfer with sfb15