I have a Keyence CCD digital micrometer (LS-7000). The application is to give a diameter of a part. The controller gives out the diameter of the part and also gives an analog output of +-10v. The PLC used is a KOYO 240 cpu with an analog input card. What I need is to convert this analog signal to give me the diameter of the part. I get a clean analog voltage but don't know how to convert (scaled data) it to mm in the PLC program. The required scale is +- 10v to +- 10 microns.
Any help in conversion of this nature will help. The exact program method of this equipment is not required. Need help fast.
Thank you!
Download the DL205 Analog I/O Modules manual HERE. They explain how to scale your data VERY well in there.
Basically though, you just multiply by 1000 to convert micons to mm... ;)
beerchug
-Eric
For any unit conversion on any PLC you can use four function math with the following, which asumes integer math:
DataOffset = Data in input register at 4 mA (or zero analog signal of whatever range - for example 0 VDC on a 0-10 VDC transmitter)
DataSPan = Data at 20 mA - Data @ 4 mA
FACTOR = arbitrary factor (multiple of 10) needed to get proper resolution and accuracy
EU = Engineering Units x FACTOR
EUOffset = Engineering Units @ 4 mA x FACTOR
EUSpan = (Engineering Units @ 20 mA - Engineering
Units @ 4 mA) x FACTOR
DATA = Actual data reading in input register
EU = ((EUSpan x (DATA - DataOffset))/DataSpan) + EUOffset
ProcessValue = EU / FACTOR
For Example, 0-60 psig from 4-20 mA with resolution of 0.1 psig:
FACTOR = 10
Data @ 4 mA = 6240
Data @ 20 mA = 31208
DataOffset = 6240
DataSpan = 31208 - 6240 = 24968
EUOffset = 0 x 10 = 0
EUSpan = (60 - 0) x 10 = 600
DATA = 18975
EU = ((600 x (18975 - 6240)) / 24968) + 0 = 306
Process Value = 306 / 10 = 30.6 psig
Thank you!!!!
I was able to get things working yesterday. It was not the plc program giving me the problem. It was the lack of understanding the programming of the micrometer analog signal.
Thanks again.
Does any1 kno how to convert raw/proportional to lbs?
18
3,623
I have a program that has a scp of 0v to Image dc and in the input minimum it has 1638 and the input max is 14736. The scaled min is 0 and the...
2,168
I am using an analog point I/O input card with a 4-20mA signal. The number comes to an INT tag. I am trying to convert the value to a percent...
3,406
Hello Experts, I am working on S5 to S7 conversion project on which stucked on analog output scaling. In S5 following logic is written for...
3,014
New to programming, please excuse what I'm sure is a long and stupid question: I'm building a training workstation with a CompactLogix. I have an...
2,797