PanelView Screen Saver Mode
RKovacic
Jul 2003
Greetings!
Does anyone know of a way to bring a PanelView out of a screen saver mode other than using a finger? I'm working with a PanelView 1000, and would like to do this when an audible signal occurs for an event that can be noted on the screen. Thanks!
Screen Saver disable.
I have not worked with the PV1000 but I have with others and I think the PV1000 will operate the same. If you select the PLC to make screen changes it will bring the PV out of the screen saver mode when the PLC makes a screen change.
Just program your event to command a PV screen change.
Roger
Out of Screen Saver Mode
It has been a couple of years since I worked on Panelviews. There is a way to change the Panelview screen being displayed by setting a number in an integer file and sending it to the panleview. You simply use a move statement to transfer the screen number to the correct integer file, based on the event that happens. We used to use this function to call up alarm screens, based on what machine went down. If the filler went down, we would call screen 1. Cartoner goes down, call screen 2... etc. That way if the line goes down the panelview is sitting on the screen that the operators need at that moment in time.
First you create a blank screen to use as the wakeup screen. Then when your event happens you first change to the blank screen, then to the screen number that you want displayed. You use a blank screen so that the operators only see the correct screen pop up. If you call an already used screen, then you will get complaints that "Everytime this event happens, the panelview goes to antoher screen before I get the right one."
I am sorry that I don't remeber the exact procedure, but it has been a while. I also think that this ability of screen number control from the PLC can be turned on or off in the panelview setup.
I hope this helps. Maybe someone else can build on this, too.
Another tip with the screen control is that the if the tags value is anything other than 0, then the PLC has control, but if the tags value is 0, then the PV has control of screen changes (allowing you to still use GOTO buttons in the PV).
In other words, what you want to do is write the value to the screen change tag, wait for the screen change, then write a zero to the screen change tag.
Have fun!
I use SYMBOLS to label the addresses in the N file for the Currently displayed screen and the PLC requested screen as SCREEN_DISP and SCREEN_REQ respectively. Then I put the following line in my program
-+-- EQU ----------+-----[OSR]-------------------+--MOV--------+---
| SCREEN_REQ | | 0 |
| SCREEN_DISP | | SCREEN_REQ |
So, whenever you use the PLC to request a screen change, and the screen actually comes up, this rung will plop a zero into the screen request register so your programmed screen goto buttons still work for the operator.
Re: Screen Saver disable.
Roger
What I have told you will do what you requested. You should also follow the other tips on keeping your "GOTO" screen buttons functioning. If you have a problem with the logic, post and I will assist.
Roger
Any good idea how to dim the display on a panelview plus performance serie b, at idel. Screen saver is not supported yet I have don it in global...
2,285
Hi. I have a used PanelView Plus 400 that already has a custom screen saver on it and I'm looking to change the screen saver I was reading the...
3,450
Hi, I have a Panelview Plus 1000 and have the screen saver set at 15 minutes. However, it has been requested that on screen saver activation the...
3,545
Ive just finished setting up a new panelview for a client. They would like to be able to reactivate the screen after the screen saver comes on via...
6,331
Hi all, I'd like to create a screen saver for a PV communicating with a MLX 1000 thru DF-1. During screen saver our company details (add...
7,362