Redundant ControlLogix secondary CPU restarting

flyers

Member
Join Date
Sep 2006
Location
Amk
Posts
295
Hi guys,

Currently, we have installed a set of redundant CLX L63 for our client, it has been running for 1++ year.

Recently, we notice a switchover and the 1757-SRM module at the primary rack showing some error COMM ERR PRT1. Referring to the manual, recommended action is replace the rack. We did that and everything back to normal.

After a while we notice that particular rack CPU is keep restarting. We measure the incoming power (240V AC) and it's normal, no flickering. Please refer to the video link below. We tried to slot in each of the module one by one, everything is fine until we connect the 1757-SRC1 cable. I guess when it sync the program from the running CPU, it cause this standby CPU to restart. Is that because of the settings or program error? We tried to add in additional 1756-IF16 module and reschedule the ControlNet, could it be the CNET files issue? We tried to inhibit and delete the 1756-IF16 from the RSLogix 5000 project tree online, but still the same.

Video clips at you tube:
http://www.youtube.com/watch?v=exkVEptAVEw

Slot 0 - 1756-L63 (Version 16)
Slot 1 - 1756-CNBR
Slot 2 - 1756-ENBT
Slot 3 & 4 - spare
Slot 5 & 6 - 1757-SRM
 
on the SRM module always show DYSQ ?

i always synch by removing the power, take the processor off, take the battery off (Clean Processor ) after that, put again the baterry, reinsert the processor, switch the power on and wualaaaaaaaaaaa they have SYNC, all the modules have the same firmware ?
 

Similar Topics

I have a redundant ControlLogix being set up. This program reads a value from a remote site which happens to be SLC PLC. Rockwell mentions SLC...
Replies
2
Views
96
I have a L82 system setup redundant that i need to download a lot of programs to in a critical environment. What is the process to do this and...
Replies
10
Views
297
Hello Experts, We have a Control logic chassis with an EN2T module for the local Panel View HMI module. Now the client asked for a redundant...
Replies
6
Views
2,159
I have a Redundant ControlLogix L61 System running on firmware 16.52. There is an existing ControlNet network for the ControlLogix IO bases but we...
Replies
10
Views
3,116
Hi. I need help troubleshooting time sync. My setup is redundant L72 Controllogix with 2 processor racks and 1 RIO rack with 1756HP-TIME module...
Replies
11
Views
4,637
Back
Top Bottom