Old July 22nd, 2021, 01:44 PM   #1
TheWaterboy
Lifetime Supporting Member + Moderator
United States

TheWaterboy is offline
 
TheWaterboy's Avatar
 
Join Date: May 2006
Location: State of Denial
Posts: 1,189
Reading the triangle ! in CLX IO

I have 4 Altivar VFDs in my IO tree that pull data from the drives. 2 are tutrned off so have the little yellow triangle. Since these are added using a "generic Ethernet module" and CIP assemblies there are no built-in tags to indicate the condition of the "module".

Is there away (GSV maybe) to test the condition of the "module" so I can capture the triangle into a tag for HMI consumption?
  Reply With Quote
Old July 22nd, 2021, 01:56 PM   #2
dmroeder
Lifetime Supporting Member
United States

dmroeder is offline
 
dmroeder's Avatar
 
Join Date: Apr 2006
Location: Vancouver, WA
Posts: 2,856
GSV:

Class Name: MODULE
Instance Name: "Name of module in the tree"
Attribute Name: Fault Code
Destination: "Your tag, DINT type"

Any value other than 0 in the destination tag is a problem.
  Reply With Quote
Old July 22nd, 2021, 02:08 PM   #3
TheWaterboy
Lifetime Supporting Member + Moderator
United States

TheWaterboy is offline
 
TheWaterboy's Avatar
 
Join Date: May 2006
Location: State of Denial
Posts: 1,189
Well that was easier than I thought. Much obliged.
  Reply With Quote
Old July 22nd, 2021, 08:01 PM   #4
ASF
Lifetime Supporting Member
Australia

ASF is offline
 
Join Date: Jun 2012
Location: Australia
Posts: 3,363
There's also another GSV attribute you can use which will give you the connection status as opposed to the fault status - running is 16#4000, anything else indicates a problem. Personally I prefer to use this because in my mind "connection OK" is "more correct" than just "I see no problems". And also you can wrap it up in an AOI if you want and get various connection statuses out of it in a human-readable format.
  Reply With Quote
Old July 26th, 2021, 09:46 AM   #5
TheWaterboy
Lifetime Supporting Member + Moderator
United States

TheWaterboy is offline
 
TheWaterboy's Avatar
 
Join Date: May 2006
Location: State of Denial
Posts: 1,189
Thx ASF.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Rockwell 1734-AENT Point IO module keeps faulting Ninja Pirate LIVE PLC Questions And Answers 17 July 12th, 2016 09:42 AM
Point IO Analog In 1734-IE2C Not reading harryting LIVE PLC Questions And Answers 10 June 5th, 2015 10:12 AM
IO field reading problem (WinCC Flexible) vojvoda1982 LIVE PLC Questions And Answers 4 November 21st, 2010 08:30 AM
Need advice on setup of PanelView+ to CLX via CNet wildswing LIVE PLC Questions And Answers 2 November 10th, 2010 10:57 AM
How many Compact Block IO or Flex IO a SLC Scanner support? ckchew666 LIVE PLC Questions And Answers 6 August 30th, 2006 01:08 PM


All times are GMT -4. The time now is 12:07 AM.


.