Hi;

I need to monitor and log the 3phase AC input voltage for which I need a device to convert AC input voltage (say 350 - 440V) to analog (0-10v or 4-20mA) to connect with PLC. Has anyone used such device? Please share the make and models number.
 
I agree that Power Meters need a different interface, but I have found that the prices have dropped a lot recently.
This is £169.00 with a modbus RTU output:
https://www.smartprocess.co.uk/mid-...tricity-meter-pulse-modbus-smartrail-x835-100
Or to go with a well known make, this is Siemens with a Modbus TCP output:
https://uk.rs-online.com/web/p/ener...ol_Gear_Whoop-_-Energy+Meters_Whoop-_-1809613
From these you can get Voltage, Frequency, Current, Power plus loads of other values.

If you just want one value then 4-20mA is the way to go. If you want more than one value then a bus connected device will give you a lot more data.
 

Similar Topics

I hope this makes sense. I need something that can accept the data from an Excel or csv file and can output a 4-20mA signal to represent this...
Replies
4
Views
2,275
Anyone have a idea of what would cause a failure of all nodes (buckets) of an AB Device Net MCC upon a power cycle of the main feeder for that MCC?
Replies
12
Views
267
Hi, I'm trying to use the IO Device Library (Product Versions) which is configured to work with the 1756-EN4TR & 1756-EN2TR but my system uses...
Replies
0
Views
79
Hey guys, I have to take an upload of a program on an S71200 PLC to change a hardware config option and then redownload the program with this...
Replies
3
Views
124
Hi, First time poster, long time reader. I've got a mass flow controller device for controlling the flow of gas. It has a flowmeter and an...
Replies
4
Views
297
Back
Top Bottom