Yes to mainly DC inputs, and all DC outputs, but most of my rack PLC projects have one 120 AC input card to monitor fused power, and if the PLC runs on a UPS to know if the incoming power has failed.

I would always use an interposing myself for this kind of thing. But i generally would only be monitoring 1 or 2 such things in a panel. For our installations typically have a "mains fail" indicator which is either a 3 phase monitoring relay or a standard 230V coil relay for single phase installations.

I do mostly water utilities work, and all our control systems are 24V powered, with a minimum of 12 hours battery backup.

Guess it's different for most other industries.
 
I would always use an interposing myself for this kind of thing. But i generally would only be monitoring 1 or 2 such things in a panel.


If there was only 1 or 2 then I would use interposing relays also.


But a line with 10 to 16 fused powers for solenoid valves and DC motor controls, as many I do have, it is easier to change one input to AC then add a bank of 16 relays and sockets and the extra wiring.
 
If there was only 1 or 2 then I would use interposing relays also.


But a line with 10 to 16 fused powers for solenoid valves and DC motor controls, as many I do have, it is easier to change one input to AC then add a bank of 16 relays and sockets and the extra wiring.

If it is easier it does not mean it is better solution or even good solution.
 
DC and probably the safest is Sourcing inputs and Sinking Outputs but they tend to confuse installers and electricians.


For all the European machines I work on this is their standard. But they always say it is because Sinking devices and outputs respond faster.


But to me the input of the PLC is not going to respond until the next scan after it turns on, unless it it wired to a Fast-DC or a HSCE input that doesn't seem to matter. And the 0.002 second faster output energizing would not make any difference in an industrial application using a Mitsubishi FX PLC.
 

Similar Topics

The past week we received a new piece of equipment from Germany which utilizes siemens controls. Typically in our company we use A.B. controls for...
Replies
4
Views
50
the conveyor can stop because of a safety sensor or safety switch. And also it can stop because of an object jam detector sensor. If the conveyor...
Replies
5
Views
133
Good Day to all of you, this is my first post, i will try to explain as best as possible, english is not my natural language. I am performing an...
Replies
0
Views
29
Hi All, Someone at work has put a PLC system on my desk, that's just been taken off an idle production line. He said "It's an S7 PLC. We don't...
Replies
10
Views
206
I have a project to automate four generator sets. The system will monitor and store the load demand of the factory. Once there's Power outage, the...
Replies
0
Views
57
Back
Top Bottom