i'm working with a differential pressure transmitter yokogawa EJA130E and have problems to connect it to a Schneider analog module TM3AI4.
I already try to wire it like the manual, also try to do a loop with the power supply and the transmitter doesnt turn on, the display remains blank.
When i connect the transmitter directly to the power supply, the transmitter turn on.
Its my first project so i'm still a newbie, i'll appreciate any help.
As the TM3AI4 is both voltage and current input, you need to configure the card in Machine Expert for 4-20mA. Its default is likely voltage input, which is high input impedance so the loop instrument won't work.
You'll need to wire the sensor loop powered like your second image if it's a 2 wire sensor.
Like this. You set the input for 4-20mA if you want the device to take care of low level and wire break alarms, you use 0-20mA if you want more control. Scale the 4-20mA to Real World values. I prefer my own scaling routine, but your PLC will almost certainly have a built in one.
Posted this to Reddit with little success, so I figured I would share it here as well. Very new to PLCs, but figured I would give it a shot to...
122
Hello Folks, Has anyone configured a Momentum high speed counter on Unity 13.1. We need the wiring diagram for Momentum High speed counter and...
76
Hey guys, the scenario is: I have already completed the drawing package for my system utilizing an A-B 440R-N23126 (Minotaur) safety relay. SoS...
139
Maybe a stretch to call this a PLC question, but it does connect to a PLC input. I have two German switches: Sick WL9LG-3P2232 And a...
109
Hello I wanted to ask some questions about the G120C drive and the protection for it. I want to control a pump, with the motor rating of 5.5 kW...
198