I had an issue with my PID control in a PLC5 today. I'm using it to keep the humidity above a certain setpoint I have the input card set up to a raw min of 0 and a raw max of 100 (the block transfer read). In the PID configuration, engineering units are 0-4095, input range is 0-100. The block transfer write of the output module is 0-4095.
We recently lost power to the PLC. When power came back on, we found the PID wasn't controlling correctly, even though the process variable was below the setpoint according to the panelview.
When I went online, I found the input to the PID was 19% as expected. But opening up the PID dialog box, the process variable in the status window said 798 (about 19% of 4095). I then went to the input max/min of the PID dialog box. I changed the max to 4095, then back to 100, and then the process variable changed back to 19 as it should have been.
Any ideas why the dialog box would have shown 798 when it was actually 19? And why changing the settings then changing them back would reset that? How could I avoid this happening again?

Thank you.
  Reply With Quote
Old October 8th, 2012, 09:25 PM   #2
sthompson
Lifetime Supporting Member + Moderator
Canada

sthompson is offline
 
sthompson's Avatar
 
Join Date: Jan 2007
Location: Vernon, BC
Posts: 1,840
It doesn't sound like you have your scaling correct. The Analog Input Card should be 0-4095, and then do the scaling in your PID Block for actual Engineering Units. This is going to make it very hard for the PID to control properly.

If you are permitted, post your PLC Code (Zip it First), and we can have a look at it for you.

Stu....
__________________
There's never time to do it right, but there is always time to do it over!
No trees were killed in the creation of this message.
However, many electrons were terribly inconvenienced.
  Reply With Quote
Old October 9th, 2012, 09:00 AM   #3
jeffblichmann
Member
United States

jeffblichmann is offline
 
Join Date: Aug 2012
Location: Wisconsin
Posts: 5
I don't think I'll be able to post the code. I think after I changed the input range in the PID block, and then changed it back again, the PID is controlling correctly now. I see what you're saying about the scaling, but since it's working now, I'm not sure if that's the cause of the initial issue. Unless when the PLC started back up after the power loss, it tried to reset to the values as you described. I've also recently read that the scaling shouldn't be changed while the process is running as it could cause a processor fault. I'm hoping to find a fix that won't require me to change the scaling because this process the PLC controls doesn't go down very often for me to have the opportunity to make a change.
  Reply With Quote
Old October 9th, 2012, 12:54 PM   #4
mellis
Member
United States

mellis is offline
 
Join Date: Nov 2004
Location: Cincinnati, Ohio
Posts: 828
When you lose power on a 1771-IFE card (the normal analog input used with PLC-5), it loses it's configuration. The PLC program is responsible for configuring the card on power up. There should be a BTW instruction doing this. Sounds like it didn't happen correctly on your power outage.

Also, if someone changed the config data for the card while the system is running and saw no effect, they might have left it that way. Next power cycle, changes go into effect. This assumes the BTW only operates on power up.

BTW scaling to anything other than 0-4095 on the card is throwing away resolution. If you scale it 0-100 on the card (I expect that is 0-100% RH), then that means your signal jumps in 1% increments. i.e. increasing humidity from 49% to 50% has no intermediate values.

Last edited by mellis; October 9th, 2012 at 12:59 PM.
  Reply With Quote
Old October 9th, 2012, 01:36 PM   #5
jeffblichmann
Member
United States

jeffblichmann is offline
 
Join Date: Aug 2012
Location: Wisconsin
Posts: 5
I do have a BTW that should be configuring the 1771-IFE. I believe when I first added it, I inserted the card into the IO configuration and it automatically generated rungs for BTW and BTR. Is there anyway to ensure that the BTW runs on power up?

What you're saying about the resolution makes sense to me. I would like to change this now that I know, but I don't want to risk the processor fault. For what we're doing, 1% increments is okay, but I'll keep your suggestion in mind.

Thanks.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Level Control PID for Duty & Assist Pumps MorphuisOGrady LIVE PLC Questions And Answers 10 March 19th, 2010 07:27 AM
PID control hapetter LIVE PLC Questions And Answers 4 February 18th, 2010 04:37 PM
PID control of motor drive considering the diameter and an external Potentiometer rajesh_gklm LIVE PLC Questions And Answers 2 January 16th, 2010 12:19 AM
DC Motor Control with PID gimmephone LIVE PLC Questions And Answers 3 March 20th, 2006 09:30 AM
PID control programming using PLC debojit LIVE PLC Questions And Answers 1 January 13th, 2006 02:33 AM


All times are GMT -4. The time now is 02:41 PM.


.