Panleview 600 factory reset
To recover from a firmware update failure, for example, fatal code 0F, you need to
restore your terminal to its out-of-box, factory default state.
Follow these steps to restore factory defaults from Maintenance mode.
1. Press and hold the DEFAULT switch on the back of the logic module.
2. Press and release the RESET switch.
3. Release the DEFAULT switch.
The maintenance menu is displayed.
Maintenance Window with Safe Mode Selected
default button pressed, please select maintenance options
Maintenance Menu -- ver 0x.xx
Special BOOT Action - SAFE Mode
Reboot with selected options Selects the special BOOT
action that will be
executed during this system
boot.
- SAFE mode-------------------------
The system will start in the
configuration mode of
FactoryTalk View ME Station.
- IMPORTANT-------------------------
will load at start up not
the custom HMI application.
The HMI application will
start normally the next
time the terminal is rebooted.
The version refers to the
boot loader.
TIP Terminals require an attached USB keyboard to navigate in Maintenance mode.
154 Rockwell Automation Publication 2711PC-UM002C-EN-P - March 2015
Chapter 8 Troubleshooting
4. Press the down arrow on the keyboard to select the following option:
Special BOOT Action -None
5. Press the right arrow three times to select the following option:
Special BOOT Action - Restore Factory Defaults
6. Press the up arrow to select ‘Reboot with selected options’.
7. Press Enter on your keyboard to initiate the factory default restore process.
The terminal is returned to its out-of-box state, including the firmware,
registry, file system, and storage areas. All user data is lost after the restore.
For a PanelView 600. 2711-B6C1 ( Standard PanelView) See text
But all you need to do is load a new program, it will write over the old.
Thanks Mickey. It looks like it worked.
This is the RIO module, we talked about it few weeks ago.
I ordered a RIO scanner card. I managed the scanner card to go OFF the fault, but never
was able to run it. Now iam trying to do that.
Bought a 2Gb memory card, did not work. I just want to have it up at least to communicate with it...
On the PV 600 now I have the fault flashing.
Sorry about that, I did a search on Rockwell for PV600 and didn't notice the manual that came up was for the PV+
No problem, I appreciate your willingness to help.
I managed now to reset, but the red Fault LED is flashing.
What now? it is the RIO version. Cable connected. Need to address it properly...
I guess. ANy help is welcome.
Have you tried to connect to the RS232 port using RSLinx. And load a new program
Straight thru cable. DF1 driver?
I just made a little program in Panelbuilder32.
Onl;y one maintained push button.
Now the settings: PV600/RIO/ Aux port:Download
PLC ype: SLC504.../Name:542/ Rack 0/ Module: 0,2/ Last chassis (check)
In block transfer: should I have anything enabled? If yes: is R or W, length?
Pass though should be checked?
Hi, I am fairly new to programming PLCs and HMIs. I have been tasked with converting a Panelview Standard application (Panel Builder 32) to...
1,639
I am trying to connect PLC5/30 to panelviewplus 1500 with 2711P/RN6 on DH+. I am plannig to load the program to Panelview on ethernet. Then I...
2,361
Hello my first time posting so hope i do not confuse you guys. I am wanting to store data from my vibration/Temp sensors that my PLC is already...
1,996
Hi, guys, how r u? There are two panels on our production line. One is PanleView 1000 and another one is PanelView Plus 1500. Can we...
2,517
Today I was tinkering with a panelview program in FactoryTalk View. The program currently just talks to one CLX processor. I wanted to pull a...
2,172