Scaling analog 4-20ma
Ones_Zeros
Feb 2014
at work
367
Hey guys i was wondering to best way to figure out the scaling of a 4-20ma signal
say for example I scale a device -10 at 4ma and 75 at 20ma
mathematically how would i check to see what i should be getting at
8ma, 12ma, & 16ma
thanks,
Hello,
output = ((input value - input low) / (input high - input low)) * (output high - output low) + output low
I normally make a spreadsheet for proofing this type of function.
max - min = span (75 - -10 = 85)
span / 16 = value / mA (85/16 = 5.3125)
(analog value - 4) * value/mA + min
8mA: (8-4) * 5.3125 + -10 = 11.25
12mA: (12-4) * 5.3125 + -10 = 32.5
16mA: (16-4) * 5.3125 + -10 = 53.75
This is basic math :).
If you'd like more of an explanation in plain English:
First, determine what percentage of full scale is represented by your milliamp reading.
For instance, at 8 mA: 8-4 (4 mA being the zero offset) /16 (16 mA being the measurement span)
8-4/16=0.25
And so, at 8 mA, you are at 25% of full scale.
Next, multiply the percentage of full scale that you have measured by the span of your engineering units and then subtract the zero offset.
0.25*85 (85 counts being the span of your engineering units) -10 (10 being the zero offset)
0.25*85-10=11.25
And so, at 25% of full scale (8mA), your engineering units should equal 11.25 counts.
This is what I like to use, plus it works well in a spread sheet or a calculator.
y=mx+b
m=(y2-y1)/(x2-x1)
b=y1-(x1*m)
x1=input min.
x2=input max.
y1=scaled min.
y2=scaled max.
x=input value
y=scaled output value
I believe designing these kinds of formulae were learned in junior high when I was in school back in the 1960's. Is this no longer part of learning math?
When I came through (70's) they taught us the math but left out the application part. It wasn't until I was in the service that all the bits fell together.
Learning is not needed nowadays, when someone on the internet will eventually give you an answer. Which is mostly why I don't bother helping most people out.
in my learning here of PLC programming and the like ive been doing alot of reading about analog scaling 4-20ma signals just recently. i got out of high school in 05' and ill be honest i dont remember learning anything of the sort thats been mentioned in this thread as far as formulas goes. FWIW.
As previously mentioned by Lynx777: y = mx + b equation of a line. A simple exercise in basic Algebra. I'd be surprised if you haven't seen it. Perhaps a picture will look more familiar:
well now that you mention it, that does look familiar now that i see it drawn. perhaps it wasnt the lack of me learning it in high school and moreso the lack of me needing to use it ever since 10th grade math until now. 👨🏻‍🏫
I use a app on android.
PLC TOOLS 1.2 by Mani
simply put in raw min and raw max, and scale min and max
then input the raw input you want converted.
In the literature for the card. It says scaling for the enginieering parameters can be done in the card. It shows what the raw data for 4 and...
3,352
Hello, We monitor the temperature of a pipe via a 4-20mA temperature transducer. This goes into DB135(Read Analog Inputs). The issue I have is the...
630
Hi all! I have a question about RSLOGIX and Analog input/output scaling So we have an existing controller with an IF8I and OF81 card. My...
937
I’m trying to perfect the HMI interface for analog configuration. I’ve provided the user the same options for all analog inputs, as follows...
1,677
Hi I have a modicon 984 with proworx 32 that is scaling an analog input, and I need to adjust the scaling. I have new analog input values and %...
1,729