GE Comm Req
BigJon1023
Apr 2016
Virginia
32
I have about 30 registers I would like to move over to another PLC via a COMM REQ.
They are not in any specific order, however, they are all between %R1 and %R800.
Can I use 1 COMM REQ to move %R1-%R800 therefore getting 770 registers of 0 and the 30 I am looking for?
If you're planning to use a COMMREQ to set up an Ethernet channel you can transfer a maximum of 1024 words. As far as I know, none of the available serial protocols permit that many registers in a single transaction. The maximum is 500 words when using SNPX serial. Modbus RTU and CCM are even more limited.
However, if you're going to use Ethernet and both PLCs support it, you should consider configuring Ethernet global data (EGD). That way you won't need the COMMREQ.
Hello, I have a PLC which communicates with 5 devices (Acuvim), when I download the program an error message appears in the fault table :comm req...
1,827
Hey guys. As the title suggests, I need to configure a Danfoss Aquadrive FC202 inverter, so that its logic inhibits the local command when the...
56
Hi; In a cabinet of a machine, a Fatek PLC with an Ethernet communication card is working. In the same cabinet, there is a 1 kW inverter. When...
538
After updating a panel, I inherited another PLC for my "learning lab". It's a Modicon TSX Micro. I've not worked with a Modicon PLC yet, so I...
152
Guys need a bit of help getting the instance correct for a 22comme with a PF40P. Trying to get 2 things first is the drive current amp draw...
97