I'm working on migrating some old Sinamics S120 drive units currently integrated in Step 7 5.6/WinCC Flexible 2008 RT to TIA Portal V14. It's a CU320 (*not* CU320-2) running firmware 2.6.2. I've seen Siemens' documentation on migrating the CU320-2 with a script that requires firmware 4.3 or newer - not supported on the CU320. I believe 2.6.2 HF19 is the newest firmware supported.
Is there a way to get this bad boy working in TIA v14 that isn't going to involve recreating the stations from scratch after migration?
Yes
But forget using Startdrive with Portal- it wont work with CU320
Import in the gsd files manually
https://support.industry.siemens.co...amics-s120:-profibus-gsd-files?dti=0&lc=en-US
Continue using Starter software for the drives
Is it really as easy as importing the GSDs? I feel silly if it's that simple, but I appreciate the advice nonetheless!
I installed a trial of Scout to do the migration but Starter is free so that is probably easiest. So you have to manage the drives outside of TIA still? Minor drawback. I'm not changing the programs at all, that's not my lane, I'm just moving the whole shebang to TIA and this is my current roadblock.
Your config will look something like this
Did your Step7 project use DriveES ?
You can try to migrate with hardware, I will be curious how it goes
How far have you gotten?
and yes- with your current CU320- you have to use Starter or Scout
Just download Starter- it is no charge
So far I've not done much of anything. I attempted the TIA migration and got about a thousand errors because it wouldn't migrate the drive units. I will have to import the GSDs tomorrow and install Starter and see where that gets me!
Migrate it without the hardware first
By the way- Starter has a script file that will generate gsd files (you have to download it from the Siemens support site)
It can take your existing CU's and generate your gsd file- then import that into Portal
Anyway- let us know how it goes
Ive done quite a few conversions but generally the existing hardware is old and not in the catalog anymore
If you want to - posts some screenshots of your Step7 hardware configuration
The one script I found is only for CU320-2s running 4.3 or newer firmware. Do you have a link for the script supporting the older models?
I will play with it and see how it goes :)
312
Has anyone migrated Proficy Historian data to a new server? I followed the guide to move all the data over, but when I run the utility, it stops...
77
We are upgrading our FTV ME v8.1 program to SE v12. Is there any way to migrate the alarm tags (about 600ish) from ME to SE. The import / export...
866
Can it easily be done ? We have a legacy project written on Allen Bradly 1746-l542 with Several racks of some on an extension rack and some on A...
1,776
I just want to get others thoughts on what is the biggest obstacle one faces in migrating to a newer system? For me with the few systems I have...
17
4,187