how to establish communication between InTouch SCADA application and RSEmulator500
Configure an OPC/DDE topic in RSLinx that points to the emulated PLC (you must have at least RSLinx Professional for this), then configure InTouch to talk to that RSLinx topic. Fairly easy.
THANKS alot optimus2861.
But can u explain a bit more about the emulated PLC!!!
U mean choose a Emulate PLC in RS Logix 500???
And how to config in InTouch to talk to RSLinx??
I have the RSLinx Professional and I use the RS Logix 500 and InTouch 8.0.
Thanks again.
Haven't done this before, I take it?
You need the following software packages from Rockwell: RSEmulate 500, RSLogix 500, RSLinx Professional (or better). First, fire up RSEmulate 500. Next, in RSLinx, configure a communications driver of the type "SLC 500 (DH485) Emulator driver". Choose a station number for the communications driver and remember what you picked (you can go back and look at it or change it later if you have to).
Now, in RSLogix 500, take your program that you've developed and do a full verification on it; fix any errors it reports. Then save it. Go back to RSEmulate 500. Open the program you just saved. It'll ask you for the station number; punch in any number other than the one you punched in for the driver in RSLinx. If you've got a debug file in your SLC program, be sure to punch in its number here too.
Now, jump back to RSLinx. Open the RSWho window, and look at the comm driver for the emulator you just set up. You should see your emulated SLC. Right-click on him and select "Configure DDE/OPC Topic". Give the topic a name and save it.
At this point, from RSLogix 500 you can go online to your emulated SLC, by browsing to it in the "Who Active Go Online" dialog. Note that you can't made edits to the program in the emulated SLC. You have to change your file offline in RSLogix 500, validate it, save it, and reload it in RSEmulate 500.
With that all done, set up your access name in InTouch to look at the application name "RSLinx" and the topic name of what you named your DDE/OPC topic in RSLinx.
And that should be it. InTouch will talk to your emulated SLC just as if it were the real thing.
Good day Programmers I have a RSTi-EP CPE100 Standalone Controller from Emerson as well as a STXMBE001 (MODBUS TCP/IP) as a Modbus communication...
639
Hi everyone, I need to establish the communication with two differents PLC platforms (Siemens S7 400 and Micrologix 1400) for a project. We...
3,607
Hi, We are working now days to establish communication between Compact Logic PLC and Parker HPC Servo drive via Prosoft MVI69-GSC ASCII...
4,284
If any body have the solution of the following problem, please help me out. The problem is that I have an SLC 5/03 PLC in the control room and...
6,012
I have Bailey infi 90 DCS system The composer (EWS) was unable to establish communication with ICI . I got this error message anyone has any...
474