VFD Capacitor Reforming?

Greg Dake

Member
Join Date
Jun 2005
Location
Milwaukee, Wi
Posts
550
One of my colleagues came across this note from ABB indicating that VFD's not in service for more than a year or two, depending on circumstances, need their capacitors reformed. Attached is the note...I wouldn't think this is an ABB specific thing is it? How much of a concern is there with this? I've never had an issue with a VFD in storage for an extended period of time...

TIA,

Greg
 
Pretty much an issue with any VFD that uses electrolytics on it primary DC bus. And worth paying attention to as well. Electrolytic capacitors do NOT fail gracefully nor gently if there is any plate-to-plate crystal growth or dielectric deterioration.

Excesses of temperature (especially swings) can encourage both crystal growth and dielectric deterioration.

The failure symptom (if very minor) would be bulging of the capacitor ends, or sometimes body. Slightly more serious would be blowing out the vent plug, and venting dielectric. The most common breakdown event is an extremely violent explosion, resulting in burning paper and tinfoil confetti all over, with accompanying mechanical damage to anything (or person) in the area.
 
Rdrast's comments apply to any equipment containing large electrolytic capacitors, not just VFD's. In fact they apply to all electrolytic capacitors but the effects and consequences v the practicality of actually reforming small components often makes this a non starter. Aside from VFD's the most common systems neeeding this type of intervention will be power supplies.
Andybr
 

Similar Topics

Hey guys, I know this is not PLC related but many of you are pretty crafty. I need to resurrect an old PowerFlex 700 VFD. AB calls for reform...
Replies
4
Views
2,330
Hello, first of all let me state for the record that I'm not a tech of any kind, I have limited experience with industrial automation devices, so...
Replies
3
Views
110
Sorry in advance for the long post, but this requires a little back story. I work in a facility with a couple hundred VFDs Most are in a web...
Replies
14
Views
246
Customer want to use contactor for their 5HP motor blower application. im leaning to VFD. anyone use contractor for blower application...
Replies
9
Views
215
Hi, I would like to assemble a simulator/practice booster pump system that uses PID to maintain steady water pressure under various outlet demands...
Replies
0
Views
89
Back
Top Bottom