Unity Pro I/O Scanning
Thilgs
Apr 2007
Wisconsin
We have a system with 6 Premium PLCs that are connected via an ethernet network. Communication has been established to all 6 PLCs from the SCADA network (we pass the is it plugged in test). One of the PLCs need to act as a master and needs to read 9 words from each of the other 5 PLCs and then write 6 words to the other 5 PLCs. I have been told using the I/O scanning option is the easiest way to do this. I have set up the Master to scan the other IP addresses, including my Master Object, Slave Index and length. However, I am not getting any data exchanged.
My question is this, in my "slave" devices, is my data to be stored in %MW, or should it be in %IW for inputs and %QW for outputs? If it needs to be in %IW and %QW, how do I map my data to fictional input and output words. When I simply assign the address as %IW100, for example, I get an error when I analyze/build that says "The instance is located on an address the isn't configured."
Thanks in advance for any help.
I can't help you with setting up the I/O scanner in unity, I have yet to do that. When setting it up in Proworx Nxt, I usually read/write 4xxxx registers which would correspond to %MW regitsters in Unity.
The error that you are getting about the address that isn't configured is easy to fix. Once in Controller properties, click on the Configuration tab. The State r=Ram settings on the right hand side has to be configured large enough that the address you are trying to access is listed.
i.e. If you are trying to access %IW300, you would need to ensure that the numver under %IW is set to at least 300.
Hope this helps,
Stacy
Diagnostic bits
How can I know that Ethernet connections with other PLCs are not broken? Are there any diagnostic bits that show which PLCs are answering now and which aren't? Where can I find such bits?
Thanks!
Yes there are diagnostic bits, but you have to tick a box somewhere to configure them. Sorry haven't got unity with me at the moment so I'm just running on memory. Seem to remember having to use the XIP? driver. If no-one else can help I'll have a look tomorrow
Geoff
Hi there
I think the easiest way is to use global data to do this. But you can do this in IO scanning as well. I used global data to transfer words between 2 PLC's. Global data set up is so easy compared to IO scanning. Please have a look at the attached screen shots and follow the instructions. If you need further assistance I can help you.
Regards
Ranjith
Hi Schtiel
To monitor ethernet devices you need to create a tag in IO derived variables. Then you can use that tag to monitor all the devices in IO scanning table and also Global data status.
regards
Ranjith
Hello, I am using Unity pro V15. I have Quantum CPU 671 and Ethernet NOE 77101 configured. I have configured IO scanning on NOE. I have attached...
180
Hi, I have two quantum modicon PLC's over ethernet with an NOE card, i wish to read one REAL value from one PLC into another that's it really. I...
6,590
I have to set up some comms over Modbus TCP/IP to some Schneider Advantys remote I/O and ABB MNiS kit. Have been told the best way to do this is...
3,545
Hi, Could anyone help me with the following problem? The setup is as follows: Schneider M340 with a NOE 0100.2 ethernet card connected to a...
8,346
HELLO MY FRİENDS ı have problem. ı tought you can solved thıs problem for me. First of all When I checked all the cable connections of the...
405