Mitsubishi FX2 Communcations problem
Processtech
Jun 2007
Leicester
Hi All,
I have a problem with a Mitsubishi FX2n PLC, the system is set up and has been operating for over 10 years in the following configuration.
SCADA (MX32) comms via RS232 to two FX2n PLC's using a FX2n-485-BD card to effect communications, the station numbers are 0 and 1, and the communications bits are:
Hex: H6097
Binary: 0110 0000 1001 0111
Station 0 is an FX2N-64MR, interrogation of this station using GX Developer shows a communications error 'PLC/PP Comm error' further investigation shows M8062 set to 1 (Error Present) and the value of D8062 is 6201.
All cabling has been checked and is without fault
I have replaced the FX2N-485-BD card on both stations as part of the fault finding routine
The SCADA system has intermittant communication with station 1 but no communication with station 0
Soft and hard reset of the complete system has been tried, the fault on station 0 will not clear. The fault appears to have occured during a period of electrical storm activity, and I am no looking at replacing the PLC as that is the only part left.
Any advise or wise words would be appreciated
Thanks in advance
Mark Bolton
Presumably no one has altered the code in the plc ?
From memory the 485 card is like the 232 card and requires an initialisation to be sent to it on first power up basis.
For a 232 card the code would look something like this
This code is within the PLC and operating correctly to set both D8120 and D8121
Thanks for the question this has had me scratching my head for a couple of days now
You could try disconnecting the scada, connecting a cable between the 2 FX2N's and write a bit of code to pass some date between them ?
If no errors are present then its the cable/scada and not the FX2N's
Has the Scada had any updates ?
I did a job with an FX2N 232 BD talking to a redlion G3 HMI last year and even though the G3 showed comms good and they talked away without any problems i found that when going online i would get a 'PLC/PP Comm error' every minute or so on the FX but this didnt affect anything.
There are some example progs in the FX Comms Manual
You could also try upping the Retry Count and Comms Time out Values (Although if it has worked for 10 years then this shouldnt matter!)
Hi Dave,
I have tried the inter-PLC communications Station 0 will not clear it's fault at all, which is making me think that it is something within the PLC, all the code is good and has not been altered, I am getting the RX Led lit on the 485 comms card but the station is not replying due to the continuous 6201 PLC/PP comms error.
Another idea swop the PLC's and programs over to see if station 0 still remains faulty.
Hi Dave,
Unfortunately the PLCs are different types otherwise I would have tried this one is a 64 and the other is much larger, I am 90% sure that it is an internal PLC problem but am checking here and with Mitsi for any other ideas
Regards
Mark
Processtech said:
Hi Dave,
Regards
Mark
I think (and this is from memory) that the io count doesnt matter on the FX's you can run a 128 IO program in a 64 IO plc (or vice versa) so you could still try swopping them, you will just have extra wires hanging in the panel.
For Information:
Talked to Mitsi tech support, they believe the PLC has Probably been spiked and recommend next step in fault finding is replacement of the PLC
From Memory, and a very old one at that, there are some errors in the FX series that need to be reset in the program, no matter what else you do.
try using a dummy bit to RST both M8062 and D8062, force the dummy bit on then off, and see if that helps.
Like I said, this is a very old memory, I may be way off, but it sounds like you are getting desperate enough...
isn't the BD card the plug in one on the processor front?.
If so you could swap the 485 cards & see if it's the card, this would be cheaper than replacing the whole plc.
I agree, the BD boards are relatively inexpensive and can fail. I've only had one go belly up, but it's definitely a place to start.
@ Parky & RBergmann
Processtech has already been down this route and replaced both 485bd cards!
Hi I am new here please help me for my project plywood auto stacker using 3 stacker system.. i need instruction command what is it? to track the...
1,604
Have a customer that normally keeps a machine powered down, only turning it on every 2 or 3 weeks to run as needed. Last time it ran OK, today it...
2,744
hi everybody have a nice day when I download to plc mitsubishi FX2-32MT transistor unit, but me download to plc being errors. i have a question...
2,436
hi everybody again have a nice day when I upload plc mitsubishi FX2-32MT transistor unit, but me upload being errors. i have a question for your...
6,140
hey all, just got introduced to a piece of surplus equipment that my company bought, it has a Mitsubishi FX2-64M plc in it. unfortunately, in my...
3,579