bf and sf both flashing on im 151-1 interface module

gasdoc2002

Member
Join Date
Jan 2008
Location
HAWAII
Posts
3
Alohas everyone
I have a siemens interface module that causes our web press to go down. The interface module group fault and bus fault light both start flashing. The siemens manual doesn't give a description of this sequence on their cause and action list. Could this mean a bad module or profibus addressing prob? any help would be greatly appreciated.

Glenn
 
Last edited:
Have you used the diagnostics in step 7?

Hardware Diagnostics,Module Information(diagnostic buffer) from the menu PLC/Diagnostic setting in simatic manager.

This should help identify the problem.
 
Bad news. The official Siemens answer is:

Your question about the flashing code 3x SF and 8X BF.

Your modul(6ES7 151-1AA03-0AB0) is defect, you have to change it by the new 6ES7 151-1AA04-0AB0.

This flashing code is not listed in the manual.

Unofficial questions:
- Is your model an IM151-1 ver 3 or 4?
- Was your modul manufactured between 11/2003 and 07/2005?
- Does the modul's ser. no. start with S C-RN, C-RD, C-S1 ... C-S9, C-S0, C-SN, C-SD or C-T1 ... C-T7?

: )

naz.


 
C-T1 I replaced the module with same model 1AA03 which is obsolete will look into new model thank you very much for the info. Alohas

Glenn
 
A request to guide us

How can we know the manufacturing dates .
our all cards are having ser. no. start with C-S4.
What is to do to stop failure of these IM modules (6ES7 151-1AA03-0AB0)
We are trying to solve the problem your guideline can make it directional towards solution .

Shailendra
"There is nothing new under the sun but there are lots of old things we don't know."






nazareth said:
Bad news. The official Siemens answer is:

Your question about the flashing code 3x SF and 8X BF.

Your modul(6ES7 151-1AA03-0AB0) is defect, you have to change it by the new 6ES7 151-1AA04-0AB0.

This flashing code is not listed in the manual.

Unofficial questions:
- Is your model an IM151-1 ver 3 or 4?
- Was your modul manufactured between 11/2003 and 07/2005?
- Does the modul's ser. no. start with S C-RN, C-RD, C-S1 ... C-S9, C-S0, C-SN, C-SD or C-T1 ... C-T7?

: )

naz.


 
the flashing code 3x SF and 8X BF.


the flashing code 3x SF and 8X BF.

that module is not working in my system were 20 other DI/DO module connected with it but working ok with 5 DI/DO module what is the reason?


my IM module is (6ES7 151-1AA03-0AB0)

 

Similar Topics

Hello, My laptop was rebooted lost 500 & 5000 tried to re-install but need to activate, need help badly, Thanks
Replies
1
Views
781
Dear experts, I have the following setup: CPU-313C (6ES7313-5BF03-0AB0 V2.6) + CP343-1 (6GK7343-1EX30-0XE0 V2.0) communicating with Siemens PC...
Replies
7
Views
2,732
Has the thinking changed on the grounding of shields on analog instrumentation cables? A friend recently attended some company training on...
Replies
12
Views
5,247
Should I ground both sides or just one side? I've been recommended both ways. What I am interested in is reasons/arguments pros/cons if you were...
Replies
15
Views
4,860
Gems and Gents, Does anyone know if it is possible to have Tristation 5.0 and Tristation 5.2 installed on the same machine? Whenever I install...
Replies
0
Views
1,130
Back
Top Bottom