between s5 c db and s7 opn db
teh
Supporting Member
Nov 2002
140
What is diferent between S5 C DB and S7 OPN DB?
I found that when i convert the program from s5 to s7
the function of OPN DB can only execute in that
particular network and cannot call the other data for following
network.
network.
It's the same thing, no difference. But you should be aware that if you do:
OPN DB1
L DBW 10
L DB2.DBW10
At the end of that statement DB2 will be open and not DB1. Any subsequent L DBW/DBD/DBB will load data from DB2.
OPN DB1
L DBW 10
L DB2.DBW10
EXAMPLE,
AT NETWORK 2
I HAVE CALL A DB12
BUT AT NETWORK 3
L DBW 198 ( I HAVE LOAD NOTHING FROM DB 12)
WHY?
PeterW said:
What DB is "DIGITAL INPUT", as that is the DB that you are using in Network 3.
ACTUALLY IN NETWORK 3 ,4, 5, 6,7..I HAVE L DBW 198...200...240
MEAN EVERY NEKWORK I NEED TO ADD OPN DB COMMAND?
THIS IS THE CONVERT FILE DIRECT FROM S5 PROGRAM. I FAIL TO LOAD
THOSE DB VALUE. I FOUND THAT I HAVE TO OPN DB IN EVERY SINGLE
NETWORK..BUT IN S5 I DO NOT NEED TO C EVERY SINGLE NETWORK
EVEN PB CALLED THE DBW STILL REMAIN C DB 12
When you post code, please use absolute addressing - no one has to then guess at what is behind the symbol. Can you post the original step 5 for network 3 for example ?
i have do some minor modification for all D.I and D.O mapping to
DB. But my problem is for S5 i only c db for 1 time. and for s7
i have to opn db for every network... why?
Because in S5 you DO NOT open any other DB after you open DB12.
In your S7 conversion, you have placed the IO into a DB and after you open DB12, you then open DB50. So the open DB when you get to L DBW198 is DB50!!!! and NOT DB12.
EDIT:
For your info
L DB50.DBW61
is a quick way of writing
OPN DB50
L DBW61
and allows the symbolic data to be shown.
What is diferent between S5 C DB and S7 OPN DB? I found that when i convert the program from s5 to s7 the function of OPN DB can only execute...
4,395
I’m attempt to establish a communication between two simulator M580 CPUs, using a READ_VAR, I have two vitalization Windows 10 in VMWare and each...
55
I have Woodward Controller EASYGEN-3500XT and Phoenixcontact make IO CAN-CUPLER part no: 2702230, Analog Input card: 2861412, Analog Output Card ...
39
Hello Everyone, I have a issue with communication between two different PLCs. So here is the facts, The Master PLC is Guard Logix 5069 with IP...
98
126