SlC500 5/04 to PV600

alondra007

Member
Join Date
Oct 2008
Location
Lake Mary, Fl
Posts
18
How do i setup the slc500 5/04 to talk to the pv600(2711-K6C9) thru the rs232. How do i setup the nodes and how i make a cable to conect them.

Thanks, for any info, i am stuck here.
 
First of all, your PV has an RS-232 port that uses a DH-485 protocol.
So the PLC port (CH0) should be configured in that mode (default is DF1 protocol).
Then, you have to configure your panelview using Panelbuilder32 (usually it is node 2 on the networks by default);
you may also view/change the actual settings for the PV inside its Configuration, at startup.
Remember that your downloaded configuration overwrite these settings by default.

Below is some useful (I think :) ) screenshots.

pvp.jpg

Remember also that you have to use RSLinx Classic DH-485 driver to connect to both devices.
Here another screenshot on that:

rslx.jpg



Hope this helps....

- [font=comic sans ms,sans-serif]fuzzy logic[/font]
 
Last edited:
Thanks, i will try this tonight and i wil let u know.

Another question when i am installing the driver for RSLinx i get the message that RSLINX IS IN SERVICE MODE, REMOVE SERVICE MODE AND TRY AGAIN.

How do i remove RSLinx from SERVICE MODE?
 
alondra007 said:
Thanks, i will try this tonight and i wil let u know.

Another question when i am installing the driver for RSLinx i get the message that RSLINX IS IN SERVICE MODE, REMOVE SERVICE MODE AND TRY AGAIN.

How do i remove RSLinx from SERVICE MODE?

Start -> Programs -> Rockwell Software -> RSLinx -> RSLinx Classic Launch Control Panel.

Stop the RSLinx Service and uncheck the "Always Run As Service" box.
 

Similar Topics

I cannot add SLC500 analog input tag (I: 8.3) to EZSeries Touch Panel Editor (V 5.3). I used all the listed tag datatype but it all says "Invalid...
Replies
10
Views
292
can the slc500 5/05 send a email and text over Ethernet ?
Replies
3
Views
195
Hello, did anybody know, if there exist an converting cable like the1492-CM1746-M01 (for an 1746-IB16 to an 5069-IB16), for an 1746-HSCE to an...
Replies
3
Views
400
Customer is buying several spare 504 CPU's to have one handy when there's an issue with the ones in operation. Having them on the shelf for years...
Replies
15
Views
2,861
You have to go offline to create the 'Trend' but do you have to download the program to go back Online with the Trend ?
Replies
0
Views
350
Back
Top Bottom