Can someone please point me to some U.S. law or code which dictates that machine safety functions (e-stops, guards, etc) cannot be run through a standard PLC, and must be either hardwired or attached to a safety-rated controller?

Yes I know it's common sense but some of my co-workers think it's just extra work and expense. "Why not just wire the guards into the PLC?" they say. I have a very large project coming up that will require zoned safety, and I have to be able to justify the extra bucks for a safety PLC or something similar.
 
NFPA 79 would be a good place to start. ANSI B11 (not sure which subsections) also have information on safety and emergency stopping. I believe OSHA has requirements as well but again it's been too long since I've sifted through it to point out the correct sections you would need.
Basically you can't use a standard plc as a safety device because that is not it's intended purpose. It becomes too easy to program around a safety device. ANSI B11 TR6 is developing a standards on safety controllers to be implemented hopefully next year. My boss sits on this subcommittee.
 
All I can find in NFPA 79 is that emergency stop operators must have "direct opening operation" (10.7.2.2), which I take to mean that they must physically break the circuit. No mention of guard interlocks.
 

Similar Topics

The existing plant has the CLX 1756-L62 (4MB), 1756-CNB (controlnet), 1756-ENBT (ethernet ip 10/100), 5x1756-IF16 (analog input), 3x1756-OF8...
Replies
3
Views
3,748
So I have a sort of unique situation where I'm wanting to run a PF755 from the IO and over ethernet. Of course, this comes with it's own set of...
Replies
9
Views
319
Dear Experts, We have two PLC independent PLC panels with two independent controllers , we need to make hardware splitting for some AI and DI...
Replies
2
Views
1,045
I have a pump house and a tank well over a mile apart. The pump house is hardwired to the tank via direct buried telco cable. Mind you this was...
Replies
7
Views
2,737
Does a hardwired 120 VAC machine need a local disconnect and lock out device? I was always under the impression that it did, but a plant controls...
Replies
4
Views
2,105
Back
Top Bottom