absolute encoder and compact logix...
darrenj
Feb 2005
Ottawa
1,003
I have an automation direct absolute encoder and need to connect it to a compact logix processor, I see the HSC will not support absolute so i see 2 options,
SSI card
or
Wire the encoder to a fast speed input card (1769-IQ16F)
i would prefer to use the IQ16F but am unsure how to connect my encoder to the inputs...
any thoughts??
Darren
EDIT.....part number for encoder is TRD-N720NWD
720 pulse per rev, 10bit grey code
Typically, an absolute encoder will connect to multiple points on a standard DC input card.
http://www.automationdirect.com/static/specs/encodermda.pdf
A 10 bit encoder would occupy ten input points, and you simply convert that group of bits to its decimal equivalent.
I'd suggest that you wire the encoder to the first ten inputs of the card to avoid having to shift the bits over. With ten bits, you can do a MVM (Masked Move) to get only the ten bits you are concerned with into an integer all by itself. Since yours is gray code, there will be some further conversion required.
I believe there may be a built in or add on instruction to do this for you.
Paul
Hi, I am looking at doing a control upgrade for an old packaging machine. It uses an absolute encoder measuring 0 - 360 degrees for each cycle of...
4,031
Hello. An absolute encoder on a rotary axis gives values in range -2147483648 to 2147483648. When value is > 2147483648 , the encoder value is...
20
2,330
I have 2 Absolute Encoders 8192 steps per Rev. (Model TR Electronic CEV65m-11003) These Encoders communicate to the PLC5-60 via Parallel push/pull...
1,524
Hi guys I am new to Encoders, so I have limited understanding of how to actually configure it, to the situation that I am in. Using this Absolute...
1,599
Hello to you all! I hope there is someone who can clarify some things to me..... Equipment used: TM PosInput1 (6ES7138-6BA00-0BA0) to read the...
1,275