SLC5/03 (RJ-45) to Panelview 600 (D-9) DH-485 comm cable
Rule #1 of all PanelView questions is "post the complete part number".
If your PanelView has a DB-9 serial connector, it uses RS-232 and cannot be directly connected to the 8P8C RJ-45 style connector on an SLC-5/03 controller, which is RS-485.
Post the complete part number of your PanelView and Forum members can help you determine what kind of converter or interface device is necessary to connect it to an SLC-5/03 controller.
See Picture and PDF's below for harware and cables needed.
  • 1761-CBL-AS03 & 1761-CBL-AS09 Cable Pin-Out.pdf
  • 2706-NC13, 2711-NC13 -NC14 _ Cable Pinouts.pdf
Or connect your PV to the SLC5/03's serial port ( configured for DH485).
See Picture below for cable
Thanks for the great information guys, but something still does'nt make sense to me. Why would I need to use the SLC5/03 RS-232 port configured as DH-485 when the RJ-45 port IS a DH-485 communication port? I also don't see why I would need a NET-AIC in between as I do not need to bridge to/from DF1 at all. The DB9 on the PV600 can talk DH-485, the RJ-45 on the SLC is a DH-485 comm port, why is this not one on one, just like the RS-232 port configured as DH-485?
Because AB says so!... ;)
Seriously though, it's because the RJ45 uses RS-485 (not to be confused with DH485), while the DB9 uses RS-232.
At least that's MY understanding... :confused:
-Eric
The reason I subjected the RS232 port on your SLC as an option is because you would not need extra hardware. Just a straight thru cable.
And as Eric pointed out the AIC is not a protocol converter its a RS232 to RS485 converter as well as an (RS232) isolator.
most misconceptions is that one is an electrical standard..and the other is a protocol used for communications.
And this is the best solution so far if I really would have to use a NET-AIC to use the RJ-45 port, but that still does not make sense to me that I can't use the actual DH-485 port the same way...
As robo77 said, DH485 is a protocol. Yes, both devices speak DH485, but the wiring is different. This means that they can't be electrically connected together. RS-232 is a 3-wire system, while RS-485 is a 2 wire system. They aren't electrically compatible. Omega has a pretty good explanation HERE (ignore the RS422 stuff). Especially look at the wiring diagrams at the bottom.
EDIT: I found a decent explanation on YouTube... http://www.youtube.com/watch?v=OvRD2UvrHjE#t=0m38s
A poor analogy, but think of it like the USB and the DB-9 ports on your computer. You can use either one to program most PLCs. Both are serial devices, but you can't wire a USB port directly to a DB-9 port. You need to use a converter. Yeah, I said it was a poor analogy... :rolleyes:
-Eric
Actually DH485 is both a protocol and an electrical spec.
DH485 = DH485 protocol
DH485 = RS485 electrical spec.
kinda of agree but can't you use rs485 and modbus RTU(protocol)
so the = would not be totally exact. :) but yes dh485 can use rs485
Does anyone know if it is detrimental to use a FULL straight through cable to connect these two. I know that the AB cable does not carry pin 9...
1,976
I have been searching past posts and manuals and I'm not understanding the mapping process. I have a SLC5/03 with a PanelView 600 and 1747-SN RIO...
4,867
Hello,:) This is my scenario the ethenet of the slc is connected and the rs232 port is to be connected to the panelview. will the panelview...
4,584
Hello all, I'am starting to experiment with an pv 600 (2711-C6C9)and a SLC 5/03 processor.I have a few simple questions and need a few tips to...
3,342
Hi guys Unbeknownst to you but knownst to me I have used little clues from the forum and I managed to solve my issue. Now I'm no n00b on AB gear...
23,412