booted off line when accepting edits in logix 500

Join Date
May 2008
Location
west central az
Posts
61
i'm having an issue wiht online editing with logix 500 version 8.200.00 cpr9 build 13, i have a 1747-L551 processor that i'm doing online edit in over ethernet and after i edit, accept and test all is good. when i go to assemble the edits it boots me off line with the processor to off line mode. 🔨 any ideas or help would be greatly welcome and appreciated from all the wonderfull knolageble guroos here.

:geek:
 
Do you have more than one copy of the program open. ?
Is another PC online to that PLC. ?
Is some one else currently doing editing. ?

These are only guesses, that could easily be remedied to see if they make a difference.
 
only one copy of teh program open, i'm the only one here for our department and the only one active. boss is gone adn coworkers are gone. there is a panel view 1000 hooked up via other comunication on a dh485 card.
 
I remember something about this when trying to do Online edits with the ML1100 over ethernet.

It had to do with RSLinx opening one connection to view the ladder online. Then to assemble changes it would open a second connection. The processor, to protect against two people trying to edit at the same time, only allows the first connection to make edits.

There were a few options you had to change in RSLinx to make it work. There was a knowledgebase article on it.

It's 32963 on the AB Knowledgebase. Unfortunately it says access level Tech Connect, so I don't think I'm allowed to copy the detailed info to here. But I think it's alright if I say you have to change the CIP options to only allow one message per PLC.
 
I had the same problem and the info from the Rockwell site solved it. It was something about the "max # of connections" in Linx if my memory serves me right. What ever it was, I remember it being easy to fix.
 

Similar Topics

RSLogix500 v7.10 XP-Pro SLC5/05 - connected via Ethernet through corp network This is for a colleague - I've never seen this before. While...
Replies
4
Views
3,644
Hi, I'm trying to import a Rockwell/AB EDS to Beckhoff but I'm not sure how to import/install the EDS. It is a PowerFlex 525 EDS. Is there a way...
Replies
1
Views
99
I'm trying to integrate a Beckhoff IPC with a Controllogix PLC. There is some documentation, on the Beckhoff website, on how to do a PLC-PLC comms...
Replies
0
Views
102
Hello..I am new to Plc.I have Mitsubishi Melsec Fx3Ga-40MR PLC controlling a machine for packing powder.Currently the Plc has issue which power...
Replies
3
Views
164
Hi, I have a 1500 that controls a station with diferents warehouses, but i also have a 1200 that controls one of those warehouses, i have been...
Replies
9
Views
292
Back
Top Bottom