SCL-500 stange Major error
pablo_660
Mar 2010
Quebec
Hi, I had this major error (558h) about the module in slot 5.
The module is 1746-NI8 and the CPU is SLC-500 1747-L553.
The manual of the module doesn't refer has this fault. So i don't know why this error is occured.
I cleared the fault and the plc is restarted.
I set to 1 the bit S:1/8
Before the plc had running without problem for 6 months.
What do you think about that ?
I have just seen this for the first time a month or so ago at a customer that had gone through a strong thunder storm (also on NI8 module). The PLC would stay up for differing amounts of time before faulting. I can only assume that there was some type of damage from lightening that had compromised the integrity of the module, but would allow it to operate for some period of time. We replaced the module and the problem has not been back. I asked them to send it to Rockwell for a diagnosis since they have been having problems loosing analog modules in that control panel anyway. We have not heard back yet if there was any definitive results.
Darren
Fault xx58h means that a specialty I/O module has generated a "generic fault". The card fault bit is set (1) in the module’s status byte.(xx = slot number)
Recommended steps
  1. Move the module to another slot
  2. Recycle power
  3. If the problem persists, replace the module
- fuzzy logic
hi
We have a spare module, so we will replace it.
Unfortunatly we can't move the module to another slot, the rack is full..
Thanks so much for your help
Hi everyone, I am new to this amazing world of PLC, well... I mean, in practice, since I already knew electronics, programming languages, IT, and...
664
Hi all, This is my first post; I am new to PLC Controls stuff and English is not my native language, so I apologize in advance if something is...
518
Hi guys. I have a challenge that I'm struggling with and I can't help thinking there's a really easy solution. I want to move a series of...
18
5,866
Hi guys! Is there a document somewhere that states the difference between SCL in TIA portal versus SCL in classic Step7? I want to reuse some...
3,158
Hi there, we have situation a compressor unit PLC faulted, the cause is unknown as it lost coms before it was taken offline by unknown reason...
1,968