SLC 500 online edit
cornbread
Feb 2007
madison, indiana
407
I'm having problems with a SLC500 that usually will kick me off line when I try to do a on-line edit. Last week I wanted to change XIC to a XIO and when I tested the edit...bam kicked me off. I have other SLC500s on site but this is the only one that gives me trouble. Is there something in the set up of the processor?
Which SLC 500? What comm. methd are you using? Also how full is the memory on the SLC500?
What exactly are the error and when are you gettng them? I had the same issue at a custeomer site a couple of years ago. There is a technote: 32963 - On-line Edits Using AB_ETH or AB_ETHIP Drivers Fail. You will need a tech connect contrat for this though. This describes how to set some CIP settings in RSLinx. It worked for me.
Double check inside RSLinx - Communications - Configure CIP options to have the following settings (see image), needed for SLC505.
- fuzzy logic
It is an RSLinx configuration issue, not a Logix problem or PLC problem. Do what fuzzylogic suggested to have RSLinx properly configured. There is a technote on the subject on AB's knowledge base. If you have techconnect then search for CIP and you'll find it.
No need for a tech connect. It's for everyone ( at least when I got it it was)
See PDF below
See PDF below
Well, unless it's a different one:
Access Level: TechConnect
Date Created: 09/16/2005 12:00 AM
Last Updated: 04/26/2011 02:09 PM
It's the same technote except for the "Access Level" and "Last Updated" fields. Why they lock down an answer like this one, I cannot understand.
Good Morning , I need to make a online change to a SLC 500 5/05 . Is it safe to turn the key from Run to Remote with causing the processor...
1,888
Good Afternoon, I'm trying to do online edits on a SLC 500 5/05 . After I put my instruction in , I keep getting " Test Edits Failed " ...
3,789
Do I was able to configure a driver and get online with the plc and found an original program error from 1995 which they would have never noticed...
5,422
Good Morning , I have a SLC 500 rack with a 1747-L542 CPU and 2 DeviceNet scanner cards. I am having a terrible time going online with this...
4,389
ok i made a cross over cable i am connecting a non serial laptop to a 5/05 slc proc anyone tell me what or how to config drivers to go online? thx
2,557