RSLogix 5000 DINT
pcola
Nov 2005
pensacola, fl
22
I have a DINT tag and a Real tag that counts to a maximum of 67108864. It is same for both a real and a DINT. What is the reason for the cap?
The DINT counts in integers only (both positive and negative).
The Real's seperation between counts if very VERY small for very small numbers and gets larger as the numbers get larger. At the point you mention the seperation between counts gets GREATER THAN ONE. So it's not good to use a REAL if you want a continous count of single items. The Real is good for AMOUNTS, the DINT is good for COUNTS.
They both have their uses (and incidently both take up 32 bits) but you must be aware of them.
I'm guessing at what you mean by "cap"
http://en.wikipedia.org/wiki/IEEE_754
Most 32-bit logic controllers, including the ControlLogix, use Single-Precision Floating Point to encode floating-point values.
Because floating-point is necessarily an approximation, when you add a small number (like 1.0) to a large number (about 7 million), the approximate value of the small number is zero, compared to the large number.
This is why counters or "totalizers" that use small increments should use Integers if at all possible.
I guess I over-assumed your question :) .
The Count Up (CTU) instruction will count to whatever the Preset value is. The Preset is a DINT datatype, so the maximum value is 2^31 - 1 (2,147,483,647).
What instructions are you using; CTU, ADD, or something else ?
I am using an ADD block to count rotations of a roll. I am adding a Real number (because of a gearbox ratio 3.12)to the DINT. I am not using a CTU. I tried using a real to see if that would help, but both of the sums still stop at 67108864.
I over-assumed also. Can you detail the particular ADD instructions and the values in both methods? Could there be some conditions to the ADD which no longer fire at that level?
Yes - and thank you - I have Tag L55_4004_D17 (DINT) that is added to a real (L55_4004_AUXR13) which is always 3.12 (gearbox ratio). The sum is then displayed to the operators so that they can change the sleeve of the roll after a predetermined number of rotations. This is the longest we have used the sleeve, and generally don't approach this high of a number. So the ADD Block is configured:
Source A - L55_4004_D17
Source B - L55_4004_AUXR13 (always 3.12)
Dest - L55_4004_D17
That is the whole calculation.
When the operator pushed reset, the L55_4004_D17 tag is zeroed out, and starts at 0, then 3.12, 6.24, ...
I tried using a real, but it performed the same way. I did this because I thought there might be a limit for adding reals and DINTs.
I appreciate your time on this.
It's the same problem. 1.0 becomes insignificant to 7-million-ish, while 3.12 becomes insignificant to a larger number.
You'll just have to find another way to calculate the number of rotations.
ControlLogix auto-converts data types in the ADD instruction, so REAL + DINT = REAL is a valid way to perform an ADD. The problem remains one of IEEE 754 notation and the fundamental way that floating-point values are handled in microprocessors.
Wait, the tag L55_4004_D17 can't be a DINT and have values of 3.12, 6.24 and so on.
Could you just count Motor Rotations by 1's, then perform a single MUL instruction (Motor Rotations x 3.12 = Spindle Rotations) and display that value for the operators ?
You are correct, but the L55_4004_D17 rounds the number to an integer. The Voith Handbook has all the values in rotation of the Roll, and not the motor, so Operations wants the value in Sleeve rotations, even though they could multiply it by 3.12. Anyway, I was more interested in why it didn't work, rather than correcting the Operator display. That is why I tried adding two reals instead of a real and a DINT. The results were the same. I could find nothing in Rockwell Literature concerning any limitations, and a web search for the problem didn't generate any satisfactory explanation. So that is when I posted it on the web site. Thank you for your time and sharing your experience.
The processor can't really add a float to an integer. It can add a float to a float or an integer to an integer. So when you add a REAL to a DINT the processor will first converted the DINT to a Real in the processor, then perform real addition, and finally convert the result to a DINT and save it to the DINT tag. Hence you still have the 224-1 (16,777,215) resolution limit for counting by ones.
This limitation is not unique to PLCs. Even 64 bit machines ultimately have a break down in resolution with real numbers.
Edit to add:
There are a number technote about this limitation in the Rockwell Knowledge Base. Refer to documents 7765, 59372, 29562, 18209, 29562.
To be pedantic, the CTU (or CTD) instruction is just a counter, and WILL continue to count after the preset value is reached. The Preset is just used to determine when the "done" (.DN) bit is turned on. You will often see A-B counters with a Preset value of zero, i.e. just being used as a counter, and making no references to it being "done"
Hi! I had a little problem yesterday regarding how to link two DINTs together, but after some time thinking, I feel my question is actually, “How...
29
7,165
I've always been a bit confused as to how RSLogix 5000 converts between data types of floating point to whole numbers. For the application I am...
12,090
PLC Programming Noob here... Converting a Micro/WIN program to RSLogix 5000. Anyway to do an Unsigned DINT in RSLogix 5000? Have a value of...
4,247
Hey all, I've reviewed many threads regarding converting one data type to another and I have something I'm working on that I'm stumped on and...
5,922
Hi Everyone, Im here to ask how to convert DINT to REAL. Im using modscan32 to inject current & read from 2 word address register, eg: 40001 &...
31,630