AB PVP to 5/04 via DH+

bigbuckaroo

Member
Join Date
Apr 2009
Location
Wisconsin
Posts
114
I am thinking of replacing an exisitng standard Panelview 1000 communicating with a 5/04 via DH+ with a Panelview plus 1000 utilizing a 2711P-RN6 communication module. Can anyone share their experience with doing something like this? Good? Bad? Any gotchas? Tips? or Tricks? Thanks in advance for any advice. Tom
 
Last edited:
The above posted link, starting at page 5-3 (Setting RSLinx Enterprise data servers), contains information about setting up the communications for a FTVS application.
Make sure that the name of the shortcut pointing to the SLC controller is identical to the one listed between the double square brackets of any of the non-system HMI Tags "names" in your imported project.
This is a pretty criptic and seemingly "complicated" process for a "first timer" and RA could do a better job when explaining it.
Once you do it successfully a few times it will become a routine...okay...almost...:nodi:
 
Got a link that deals specifically with the 2711P-RN6 besideds the installation instructions? All the searches I am doing only find that.
 
Just to follow up I did get this working. I will explain what I did to benefit others who may have a question. The comm module itself is indeed plug and play but there are a few more things you need to do in order for it to work on your DH+ network. The following assumes you have a working project in Factory Talk ME. Open Communications Setup and then right click on Rslinx Enterprise on the right side of the screen. Select Add Driver. Select DH+. Set the station number and baud. After the DH+ driver is created, right click on it and select Add Device. Select appropriate device from list, 1747-L542 SLC 5/04 in my case. Select the address from the drop down list for the node you want to communicate with. Click OK. Create the Runtime file and download it to the PanelView Plus. Hook up your DH+ cables and verify you are communicating with the PLC. Hope this helps.
 

Similar Topics

Hello, I made a small change to my FTV ME file (added an ack-all button) and re-downloaded to my PVP. Since then, when the application starts up...
Replies
8
Views
1,025
Hello everyone, I'm seeing Japanese characters with a 90° rotation on a new PVP+7 screen. I post here hoping someone has encountered this issue...
Replies
4
Views
760
I've got a relatively simple standard system with an issue that is frustrating us. Upon powering up the system as a whole, sometimes the Ethernet...
Replies
3
Views
632
Hi all, This is not a call to arms. I am submitting this solution for those who find this thread because they experience the same issue. I...
Replies
0
Views
652
Hi all, i am running a PVP1000. The details are as follows: CAT: 2711p-rp6 Firmware: 5.00.04.55 (CPR9) I bought this version of PVP logic...
Replies
10
Views
2,136
Back
Top Bottom