S7-400 PLC Fault
isteak007
May 2009
NewYork
216
We have a S7-400 system.
which Power Supply (PS407 4A) is totally defective. So i replace it with
PS407 10A. after downloading the new hardware configuration to the CPU. CPU comes to run mode. but EXTF Led is on and BUS2F Led is Blinking
So i checked the diagnostics buffer. it seems to be a profibus fault.
Can anyone give me an idea?
Here is more information in attached file.
  • Diagnose_fault.txt
Go to HW config, open it in online - look for modules that are not present on the bus.
I/O access error, writing
P area, word access, Access address: 544
FC number: 3
Module address: 238
And also it a H system ? For the rest of errors like
I/O access error when transferring the process image to the output modules
Look there:
http://www.automation.siemens.com/WW/forum/guests/PostShow.aspx?PageIndex=1&PostID=19661&Language=en
DP Slaves are all missing. but physically they are all present.
Something caused the PSU to become defective.
Could it be something that damaged other things ?
If you connect your PC to the DP port (*), can you see the CPU ?
Can you see the slaves ?
*: The DP connector in that port must have a piggy-back PG socket.
I guess DP port of the CPU is defective. Because I can't communicate with the
CPU using DP port. PC Adapter (Profibus) mode.
Any Idea?
Here is a suggestion for a fix if you dont have a spare CPU and you are desperate to get up and running:
You have a 412-2DP CPU.
It has an MPI/DP port and a DP port.
The MPI/DP port is setup for MPI, and all the i/o hangs on the DP port.
You can reconfigure the MPI/DP port to DP, and move all the i/o to that port. Depends on what else the MPI/DP port is used for, but it can be the solution.
Any Idea?
I have experienced a defective DP port ONCE. It was caused by 230V on the DP bus from a faulty terminated Simocode.
You must check the DP equipment thoroughly, measure, look and sniff.
Kalle
Well I am desperate to run it,
MPI /DP Port is used for HMI as MPI Network.
If i configure it to DP port. What will happened to HMI. Because HMI is using the MPI network
Production is Stop, lot of pressure, and everyone believe i am the responsible one
Maybe switch the HMI to DP as well ?
And then run both i/o and HMI parallel on the same port.
What kinf of HMI is it ? Do you have the source for the HMI as well ?
OK, it is a HMI Panel with a proprietary software onboard.
Without the source code and the programming software you are stuck.
What you can do:
You can contact the original manufacturer of the machine and ask for help.
Or you can get a spare CPU asap. But... I am not 100% convinced that the problem is with the CPU, or with the CPU alone.
Hello Experts, I would like to seek advise on how or what tag i should use or do to get the PLC diagnostic buffer to know what is the root cause...
5,645
Hi friends,I have a machine with Micrologix 1400 PLC and My PLC goes to fault mode every 7-8 days, and error i see in PLC Fault code is MAJOR...
5,383
If and when a PLC faults (front LED solid or blinking), is there a single bit that is enabled, or do I need to monitor all the bits listed in the...
2,308
Hi All, I am facing one issue with the SEW MDX61B drive. Issue- I want to run a conveyor with this drive in two directions but it runs in...
343
:huh: i don't know master password and i tried "1234" too but it didn't worked i want to upload new program but i think its password protected and...
988