Reason for 4-20mA current as a standard signal for transmitting data to and from PLCs

ivanlch

Member
Join Date
Jul 2012
Location
Australia
Posts
26
Hi,

What is the reason behind the 4-20mA current as a standard signal for transferring data? Well for starters, we choose current over voltage because there is less signal / data loss when the signal is being transferred over.

How about 4-20mA?

Well the purpose of having 4mA as a minimum is to be able to make sure that process actuators are "on" so that SCADA is able to detect any possible fault. Is that right?

how about 20mA?
 
just a standard that was implemented, could easily have been any other current, but 20mA was "the chosen one".

Typically these are measured as voltage across a 250R resistor, 1 to 5V dc

4-20mA can readily be sourced by devices that run off 24Vdc, and can therefore provide the current for up to 4 receiving devices in series.
 
just a standard that was implemented, could easily have been any other current, but 20mA was "the chosen one".

Typically these are measured as voltage across a 250R resistor, 1 to 5V dc

4-20mA can readily be sourced by devices that run off 24Vdc, and can therefore provide the current for up to 4 receiving devices in series.

Ok, was my theory about 4mA current correct though?
"Well the purpose of having 4mA as a minimum is to be able to make sure that process actuators are "on" so that SCADA is able to detect any possible fault. Is that right?"
 
Ok, was my theory about 4mA current correct though?
"Well the purpose of having 4mA as a minimum is to be able to make sure that process actuators are "on" so that SCADA is able to detect any possible fault. Is that right?"

That is correct, if you used 0 mA, you couldn't tell the difference between Zero Output, and a broken wire. As well, many Two Wire Transducers use that 4mA to power the unit, but I doubt that was the original intention of the 4mA Standard.

Current Loops are used due to their immunity to noise over long distances, as opposed to say 1-5VDC or 0-10VDC.

Stu....
 
That is correct, if you used 0 mA, you couldn't tell the difference between Zero Output, and a broken wire. As well, many Two Wire Transducers use that 4mA to power the unit, but I doubt that was the original intention of the 4mA Standard.

Current Loops are used due to their immunity to noise over long distances, as opposed to say 1-5VDC or 0-10VDC.

Stu....

ok thanks =) (y)
 
No problem!

Do a Google Search for 4-20mA History, and you will find some interesting stuff.

Stu....
 
Last edited:
Hi,Well the purpose of having 4mA as a minimum is to be able to make sure that process actuators are "on" so that SCADA is able to detect any possible fault. Is that right?

It's nice, but it wasn't the primary consideration for an elevated zero. The purpose of the elevated zero at 4mA is to allow a 2 wire loop powered transmitter to use 3.5-3.6mA of current to power the transmitter's electronics. The 2 wire concept of power over the same 2 wires as the signal would not be doable with a true zero based low end.

Were the low end 0.0mA, there would be no current flowing to power the field instrument's electronics.

A 'live' zero is a benefit, but it isn't the primary reason for an elevated zero.

the 20mA?
4-20mA followed in the wake of 3-15psi pneumatics.

3-15 psi has a working span of 4 times the zero offset.
zero offset = 3; 4 * 3 = 12; 3 + 12 =15

for 4-20mA
zero offset = 4; 4 * 4 = 16; 4 + 16 = 20.

Even Foxboro's current standard, 10-50mA, was the same ratio:
zero offset = 10; 4 * 10 = 40; 10 + 40 = 50

To have wide spread industrial signals use the same ratio is not a coincidence.
 
Current driven circuits will vary the supply voltage to keep current constant through a specific
load range, thus voltage drop over distance is not a factor of signal transmission degredation.
The offset from zero (4mA) represents a true analog quantity, i.e. (current flow already exists
at the value of zero). The value of current representing zero simply has to change, it does not
have to turn on, and then change.
 
I use 4-20 ma for 2 very straight forward reasons.
1) Very immune to noise/induction.
2) I can detect loss of signal if the 4 ma goes below about 3.6 ma indicating a problem/
 
Ok i have a little question so you start with 4 to 20 mA and the real world has the minimum signal going less than 4 mA or the highest signal is slightly higher than 20 mA , now the question is other than being unconventional or faulty is there a problem interpreting the signal , in as much that it may be slightly parabolic by nature and nonlinear . Now Allowing that in most applications it might be considered unrealistic to expect to use the total range of 4 to 20 mA scale . Or might the numbers be more like 8.999 mA to 13.500 mA mind you these are all throw away numbers but for the purpose of discussion only
 
One component of "accuracy" is linearity. There's not supposed to be any non-linearity or hyperbole. It depends on the hardware.

Some industries tend to care, like pharmaceuticals, where calibrations are mandated by regulatory agencies.

Others wouldn't know if the linearity bowed 15%, because they hook it up, scale it and run it.

Linearity from commercial chipcs pretty good, even in the low end A/D and D/A's. Otherwise they chip people couldn't stay competitive.

Here's NAMUR's (German standard) map for 4-20mA:

qpf9r5.jpg
 

Similar Topics

I've posted this on the ptc forum as well, but no luck with an answer (waiting for my service contract number) I keep getting the following error...
Replies
2
Views
129
Good Afternoon , I have a Powerflex 70 Drive . It faulted out with a #12 HW OverCurrent Fault . With your experience , what is the...
Replies
5
Views
7,778
UL 508: Any reason I can't supply a 60W 24VDC power supply from 2 legs of 480VAC? Our MechE is asking, it is for a product I don't deal with. My...
Replies
12
Views
5,881
Hello, I am having an issue with 1756-IT16 modules going out at a client’s location. This has been the issue from the very start. The modules will...
Replies
0
Views
938
Hi guys, First post here but i really need your help on this Devicenet communication error. I have 5 electrical panels wired the same way, but one...
Replies
6
Views
2,830
Back
Top Bottom