Desert Dog,
I was traveling today, and had some time to throw together some sample code that might make the pointers a little more clear. I'll test it quickly tomorrow and post it. I included two methods to do what you describe (point to a selected recipe and copy it to the current recipe). One method calculates the pointers every time you call the function, and the other calculates them only upon startup. I hope it can be of help.
DD,
Like S7Guy I've got an alternative (very simplified) example which may help. I've attached it here as a zipped source file (.AWL) for FC19. It takes 5 parameters, all INTs : SourceDB, SourceByte, DestDB, DestByte and Length. From these it assembles the ANY pointers for source and desitnation and then calls SFC20 BLKMOV. (Make sure SFC20 is in your offline project before compiling).
I can appreciate it doesn't solve every problem, but it does at least show how to assemble all 10 bytes of an ANY data type from basic info.
Regards
Ken.
Aaaarrrggghh!
Dontcha just hate it! No sooner had I posted my code attachment than I spotted two typos in it!
In Network 3, change the reference to #Source_DBNo to read '#Source_ByteNo'; and in Network 4 change #Dest_DBNo to read '#Dest_ByteNo'
I've had a bad week so far this week, and it's not getting better.
Regards
Ken.
Here you go Desert Dog.
To test the code, put it in one of your projects and turn on Symbolic Addressing Priority.
Method 1 calculates the pointers only one time upon startup. This saves quite a bit of scan time later on, since you don’t have to calculate them every time you want to copy a recipe. This is actually my preferred method, because I can change the structure of my DBs, without changing any code whatsoever (to see this, go ahead and add some more values in the Recipe UDT, recompile the blocks, download them, and restart). To test it, stick FC3 in your startup block. It will then find the start pointers and recipe lengths and store them right at the beginning of the recipe block. Note that I find the length in bits, bytes, and words whether I need to use them later or not. Also, I use dummy values if I don’t actually need the output variable. I could have created a new function instead, but since it is called only on startup, I don’t really care about scan time efficiencies in this case.
After the PLC starts and you go online with DB5, you’ll see that many of the pointers you need for dynamic indirect addressing are right there. Looking at FC5, if I force “DB Recipes.RecipeSelect” to any value above zero, it will use these values to create a pointer to the correct recipe, and then call FC6. In FC6, we just use these pointers to format AR1 and AR2, and grab the recipe length in words for the loop counter. A couple of notes: Obviously, if you enter a value greater than the number of recipes in the block, this code will blow up, but this maximum number can be calculated during startup as well. Also, I used DB5 for all of the data, but you can easily use different blocks for the Current Recipe and the Stored Recipes. If you do that, just use an instance DB for one of the blocks. All in all, this method is very scan time efficient as well as very generic. I used names like “Recipe” in FC4 for clarity, but in reality I have a library function that uses generic terms like “InputData”, and I use it whether I’m finding pointers for a conveyor or a VS Drive.
Method 2 is closer to what you were doing. It is still generic, but it has to calculate the pointers every time a recipe is copied. If you test this, make sure you remove FC3 from the startup block first. In FC7, if you force a value in the RecipeSelect, it passes the pointer for Recipe[0], the CurrentRecipe, and the SelectedRecipe. That’s all the info we need to determine the recipe length and offset. Again, go ahead and insert new recipe variables in the Recipe UDT, and you still won’t have to change a line of code. You can even insert stuff right at the beginning of the block, and it won’t matter.
Hello everyone, I am a student and would like to take the next step and learn FactoryTalk (Batch preferably) and how to create HMIs etc. Would...
519
Hi all Trend seemed to have carved a niche in building controls. The controllers seem expensive and inflexible, in the words of a Trend user. Do...
504
I have a 24" plotter that we print out full scale backpanels and transfer all the holes to a backpanel for faster layout and build time. Does...
1,664
Anyone building cabinets according to Korean standards? What to think about? Do you need to use components with Korean approvals?
850
General question for everyone. I'm finishing up some industrial electrician training in the next couple years and then plan to open up my own shop...
1,578