Modbus rtu with rs485
abbas.a.fahes
Mar 2015
LEBANON
Dear all
I'm using Siemens plc s7 1200 and I need to implement a modbus server with RS485 to connect sensors to the plc so please if any one can help me to implement this board.
thank you
I think you need a Modbus master, not modbus slave/server.
Sensors are almost always Modbus slaves (RTU RS-485)or servers (TCP ethernet).
If your sensors are like everyone elses, then you need a Modbus Master/client in the PLC to talk to the Modbus slaves.
Modbus slaves can not talk to Modbus slaves. No way. No work-around. They're dumb and silent unless spoken to my a Modbus master.
I'm a Modbus guy, not a Siemens guy. A Siemens guy will have to help you with details.
Go to the Siemens automation support site.
Search for entry id 47756141
Its all there, amazing what a little effort can find.
I'm trying to control a device via MODBUS RTU and the ModbusRtuMasterV2_PcCOM in Twincat 3. I've configured a device with the right com port and...
259
I am trying to figure out some communication specifics for a Modbus RTU network that I will be integrating with and could use some help to make...
2,123
I'm getting no response from a device I'm trying to communicate to with a Beckhoff IPC. I'm not sure why it's not working. Attached are pictures...
645
HI guys: I am attaching several diagram from several sources, it seems to be that there is no such a wiring standard for modbus RS485 RTU. In some...
24
4,612
So I'm working on an old project I did several years ago. It has 12 nodes on a modbus RTU network. I'm going back for an expansion. I'm going to...
1,916