1747-L542B vs 1747-L552B/C

Besides the fact that SLC 5/05 uses Ethernet instead of DH+, are there any major differences between the 2 processors?

I'm about to revive a mothballed small factory that has a 5/04 in it and want to use a 5/05 for the Ethernet capability for obvious reasons. My thoughts are that there is no problem swapping the processors but wanted to check with you guys first.

Ben
 
The 5/05 processor features additional functions, but it should still support everything that exists in the old program. As jstolaruk already mentioned, you might need to modify any messaging that existed in the old program, since the 5/05 does not have a DH+ comm port.
 
Also, just a reminder that if there were any panelviews talking to the 5/04s, it is likely that they will be unable to talk to the the 5/05s unless they also have Ethernet available.
 
Thank you for the replies. No, there's no DH+ going anywhere else. It used to run to a SCADA node via an S&S card but we're replacing all that with new,,, thank goodness.
 

Similar Topics

Hi all I am working with a SLC 5/02 and having trouble getting online with it. I am using a 1747-UIC adaptor which allows for USB>serial and...
Replies
9
Views
155
I have a slc500 plc 1747-L30A. Using a communication cable 1747-PIC cable box combination. Running a version of software from DOS on a Windows 3.1...
Replies
8
Views
193
hello I am getting a 57h fault - Specialty I/O module has not responded to a lock shared memory command within the required limit. Fault randomly...
Replies
2
Views
126
We are in the process of upgrading a controls system. The existing system is a SLC500 with some IO cards and a 1747-SDN module communicating to a...
Replies
5
Views
589
se me desprendieron los cables del cable usb quiero soldarlos pero no se como van los cables si alquien me pudiera proporcionar una foto o como...
Replies
1
Views
425
Back
Top Bottom