1761-NET-DNI Replacement?
asteroide
Jul 2010
der
158
Hello Friends
I need to communicate a 5/03 PLC with a Micrologix 1400, to send and receive some bits and integers between both PLCs.
Int the 5/03 the channel 0 is used by a Panelview.
The 5/03 PLC has a 1747-SDN Devicenet scanner, so I have thought in a 1761-NET-DNI connected to the micrologix 1400.
But, 1761-NET-DNI have been discontinued from 2013. I have asked to AB for a replacement but i have not received response.
Do you know a replacement for this interface?
o maybe another way to communicate 5/03 with ML1400?
Thanks in advance.:)
Do you have to use DeviceNet? You can still get the 1761-NET-ENI until Jan 2017 so you could use ethernet between the SLC and the 1400.
Or if you can get them to pony up the money update the SLC to a CompactLogix processor.
To use Devicenet is not mandatory, just is an option that I think.
I have to do that in 2 similar machines, the other machine has a 5/04 PLC and Micrologix 1400.
The problem is that the channel 0 is used by the Panelview, when i have to connect the PC to the 5/04, I have to disconnect the panelview and when i have to connect to the panelview, i have to disconnect the PLC.
Is it posible to connect the 1761-NET-ENI through the same port than the panelview in the 5/04? (The panelview just have 1 port).
Another issue that i see, is that the 1761-NET-ENI will be discontinued in few months.
On the other hand, Could I use DH485 to connect 5/04 and ML1400 and the panelview directly? Should I use some adapter/isolator?
I have never used DH485 networks, just point to point.
Thanks again:)
Hello everyone I have a micrologix1500 connected with RS232 to my computer, and connected to the 1761-net-dni with a series connexion from the...
2,946
Hi, Getting some hands on training and putting together a Micrologix 1100 trainer that that will be used to control DeviceNet DrIves and Valves. I...
1,625
Hi ! I would like to know if it is possible to use a MicroLogix 1400 with a 1761-NET-DNI module AND Modbus RTU at the same time ? Thanks in...
4,297
Hi friends I have followed the instructions in DeviceNet Interface User Manual Catalog Number 1761-NET-DNI page 69... But Heartbeat never...
1,428
Hi everyone, i´ve done the little project and run perfectly. This is the practice in capture images. this is the first step, exchange I/O between...
2,195