Hello,


I am commissioning a 1769-L33ERMS compact guard logix 5370 safety controller and am running into an issue with the safety ethernet devices.


I have 4 kinetix servos 2198-HXX-ERS2, an armorblock 1732ES and area scanner. I'm not very well-versed in cip safey and SNN and what-not. But what I am experiencing is that when the plc is in program mode, I can communicate with and read values from the safety devices, but as soon as I switch to run mode in the plc, the safety devices fault and timeout. A repeated faulted > connecting > running > faulted pattern.
The PLC does have time-synchronization enabled and is the master.


I'm at a loss for what to look for next, any thoughts?


Edit: Code 16#0203 - Connection timed out, error on the modules


Thank you!
 
Last edited:
Update: The safety task was executing at a rate too fast for the system to accommodate, lowering the safety task interval fixed the issue.
 

Similar Topics

Hi, I have an 1769-L33ERMS that I swapped out for a spare because it was causing issues. When power cycled it would hold the Ok and Safety Ok...
Replies
1
Views
621
Hi All, I have a safety compact logix PLC. I was wondering if anyone has experience in getting both of the ethernet ports on the device to have 2...
Replies
4
Views
3,375
We had a Processor Failure yesterday. Opened a new in the box Processor, and could not get BootP to work with it. After a few hours of trying...
Replies
5
Views
204
I have a 120V relay, 120V DI card and a analog input. I was wanting to know if i could put a 24V DI and well as a 120V DI card on the same plc...
Replies
1
Views
103
Does anyone know what the data transfer rate for this series of CompactLogix PLC's? 1769-L24ER-QB1B to be exact. Cheers.
Replies
1
Views
130
Back
Top Bottom