I have tried to find this everywhere and I am really not sure what I am doing wrong. I am trying to use a CompactLogix and the message functions to read and write the inputs of a Micrologix1400 (1766-L32-BWA Ser. B) and cannot figure out for the life of me why my path is not recognized. I've read about a dozen different threads and seen tutorials and it seemed that I could select a SLC typed write/read, set the communication type to CIP, and my path would be 2,[IP address of the Micrologix], as its controller to controller using embedded ethernet for both. From what I understand, I do not need to add the micrologix into the IO tree using this method.
When configured in this way, I still have a message error of 16#0009 with extended error code of 16#0000_000c. I have attached screenshots of me online with the PLC to show what my path is and the error showing. I have not used the message instruction before but it seemed very straightforward, not sure why I am running into issues with it.
Any assistance would be greatly appreciated!
When configured in this way, I still have a message error of 16#0009 with extended error code of 16#0000_000c. I have attached screenshots of me online with the PLC to show what my path is and the error showing. I have not used the message instruction before but it seemed very straightforward, not sure why I am running into issues with it.
Any assistance would be greatly appreciated!