AB DLR Supervisor Issue
Bryd29
Mar 2024
Kuala Lumpur
Hello all. I need some help on DLR issue we encountered which is the DLR not working when supervisor is disconnected from the ring.
FIrst of all, here is a architecture of our system.
126 is configured as supervisor and 127 and 124 as the backup supervisor. This ring is healthy and normal as observed in DLR Tools.
The problem happened when the both connection to the supervisor EN2TR card is disconnected, the ring became faulted and DLR tools can only detect the 127 EN2TR.
When non supervisor EN2TR is connection disconnected, DLR tools still can detect the other Card.
Has anyone encountered this issue before? Any idea on how to solve this?
Bryde29, hello and welcome to the forum.
Can you show the DLR parameters for the main and the two DLR supervisors?
Also, did you change any of the baud rate and duplex settings. In DLR one should use automatic.
Finally, did you verify that the firmware of the 1756-ENTR/C is the same for all modules.
Hi Alfredo. Thanks for responding.
Here is the DLR Parameters. As can be seen, all the firmware for all EN2TR is the same.
As for the the baud rate and duplex setting are set to auto negotiate for all EN2TR including the ETAP.
What about RSLinx, when the main supervisor (.126) is disconnected from both sides, does RSLinx detect your nodes. If yes, there could be an issue with the DLR tool.
I think this is a limitation of the DLR Sign-On and Participant list that DLR Tool uses.
Tool uses the DLR Participant list to build the graphics, but .127 will not have Participant List built until it sees the "Normal" (i.e. healthy) ring to send a sign-On message. I don't remember if manually sent Sigh-On message will create a participant list.
To verify that, bypass .126 with a cable jumper to see if all comes back.
Hello, I have a small DLR ring set up in a lab that consists of 1 Stratix 5200 and 2 ENTR/Cs. I am having an issues only on recovery of the ring...
188
Greetings Folks, This is my first post after a long gap (almost 13 years) on this forum and i hope that i will get things fixed with your...
331
Hello, I have been trying to figure out how to connect to and monitor a DLR that is on a remote rack from my PLC. The local has a 1756-L81E and...
135
HI I have a stratix 5700 switch 1783-BMS10CGA and I am asking if I can configure it to do a ring topology. So what can I do to configure it. I...
516
Hello Everyone, What is the best practice for DLR set up. Should I keep all VFDs on one DLR and FlexIO on another or it would make sense to put...
2,686