Analog: Not should I, but can I?

You need to add wire resistance to internal components resistance....

I have seen that kind of unsafe use of 4-20mA loop with an extra power supply in the middle of the run to boost the voltage. as long as everything is isolated from ground or any system reference voltage it would work....

It is hard to point which one is worse but this is another option. You can even use duct tape to hold the extra power supply on one of the drive panel to make sure it looks odd.... :)




I would use signal isolators/duplicator to do a cleaner and safer install for that kind of things as suggested. This would also keep the signal to other components if you service one....
 
You need to add wire resistance to internal components resistance....

I have seen that kind of unsafe use of 4-20mA loop with an extra power supply in the middle of the run to boost the voltage. as long as everything is isolated from ground or any system reference voltage it would work....

It is hard to point which one is worse but this is another option. You can even use duct tape to hold the extra power supply on one of the drive panel to make sure it looks odd.... :)




I would use signal isolators/duplicator to do a cleaner and safer install for that kind of things as suggested. This would also keep the signal to other components if you service one....


Thanks for the info. Conductor resistance was taken into account, and I consider it negligible in this circumstance, as there is less than 40 feet of conductor in the entire loop.
 

Similar Topics

hello.. i wanna add the value of an analog input value to the PLC existing system in my plant, i use OMRON CS1G-CPU45 and the analog input module...
Replies
0
Views
3,699
Hi looking to install a smaller less sophisticated PLC for fountain timing and also one analog pressure sensor which would be used to detect...
Replies
23
Views
639
Hi all. I have 1793-IE4 (4)analog inputs modules in a 1794-ADN IOFlex DeviceNet Rack. I cannot find if I can I have access to individual channel...
Replies
1
Views
75
Good afternoon, I am currently working with an HMI/PLC LP-a070 and I require at least one analog output, but the PLC does not have one. I was...
Replies
5
Views
153
Hi all. Customer wants analog faceplates really bad, even if we explained that it doesn't make much sense in his process. What he wants to see...
Replies
7
Views
263
Back
Top Bottom