thanks to all those who replied me.
Please direct me to the correct way to getting some temperature reading on HMI.
i'm using 1769 PLC and panelview plus compact 400 HMI. RSlogix5000 is the software for PLC and Factorytalk View ME (7.0) for HMI.
what i need is to read 70degF(4ma)160DegF (20ma) in the PLC. i dont know how do i get this.
i tried to do it as attached.
Any reply is highly appreciated
Thanks,
Roni
Go to the AB web site and download the SCLP add on instruction. You can then scale your analog card raw data into what ever range you want.
I would start there.
Edit: sorry I didn't see that you already had a SCP AOI. If no one answers your questions I will look at this more later and post back.
Had a chance to look quickly at what you have done.
Check your input min and max on you SCP instructions. In one the min and max are the same number and on another you have the min at 20000 and the max at 4000. That appears to be backwards. Also why do you have two SCP in a row? They are both scaling the same input channel. You shouldn't need more than 1 instruction per input channel.
Hello, We monitor the temperature of a pipe via a 4-20mA temperature transducer. This goes into DB135(Read Analog Inputs). The issue I have is the...
653
Hi all! I have a question about RSLOGIX and Analog input/output scaling So we have an existing controller with an IF8I and OF81 card. My...
957
I’m trying to perfect the HMI interface for analog configuration. I’ve provided the user the same options for all analog inputs, as follows...
1,708
Hi I have a modicon 984 with proworx 32 that is scaling an analog input, and I need to adjust the scaling. I have new analog input values and %...
1,748
Hi, i've write this AOI to send a ControlValue comes from pid and control a valve. this valve is controlled through analog output. the rang of...
1,045