Does anyone know if it's possible to trigger an output with the Beckhoff EK9000 and an output card via the coupler's web interface without having a CPU or controller?

I'm new to Beckhoff controllers, any help is greatly appreciated.
 
Does anyone know if it's possible to trigger an output with the Beckhoff EK9000 and an output card via the coupler's web interface without having a CPU or controller?

I'm new to Beckhoff controllers, any help is greatly appreciated.

No, not possible. You're going to require a CPU and the TwinCAT runtime installed on that CPU module/IPC/CX. The web interface for the EK9000, although I've not used one, appears to be only for configuring the bus coupler.
 
The EK9000 is a ModbusTCP bus coupler. So you should be able to "talk" to it with a modbus master system. THis could be PLC, PC, etc. I would think that you should be able to use modpoll on your PC to read/write from/to this coupler.
 

Similar Topics

Hi, I'm trying to import a Rockwell/AB EDS to Beckhoff but I'm not sure how to import/install the EDS. It is a PowerFlex 525 EDS. Is there a way...
Replies
1
Views
131
I'm trying to integrate a Beckhoff IPC with a Controllogix PLC. There is some documentation, on the Beckhoff website, on how to do a PLC-PLC comms...
Replies
0
Views
171
Hi everyone, This is my first time posting, so please forgive any omissions or mistakes. I am attempting to control the velocity of a stepper...
Replies
18
Views
1,152
Hello sameone have Beckhoff PLC Siemens Sinamics V90 configuration example?
Replies
0
Views
125
hello, I am using Beckhoff with TwinCAT3 and when I change or add some new hardware or for any reason, there is a mismatch in the real hardware vs...
Replies
1
Views
154
Back
Top Bottom