hamark Member H Join Date Sep 2009 Location Arkansas Posts 2 Sep 1, 2009 #1 Using the 1747-SN -> ASB -> NO8I card. The Class 1 interface must be used. Only 8 words can be BTW sent to the card. The 8 words set the output values. How do you send the configuration words?
Using the 1747-SN -> ASB -> NO8I card. The Class 1 interface must be used. Only 8 words can be BTW sent to the card. The 8 words set the output values. How do you send the configuration words?
hamark Member OP H Join Date Sep 2009 Location Arkansas Posts 2 Sep 1, 2009 #2 When using the card in Class 1 mode no configuration is required.