Connect SLC 5/03 To PanelView 550
shjackson
Apr 2005
We are trying to connect an SLC 5/03 to PanelView 550. The panel gives error 612 "no active nodes". I have read other posts which talked about using an NC13 or NC14 cable. If that is the way to do it, how do we make the cable?
We have also tried using a 1747-aic+ converter along with a 1747-pic to connect. Panel is unable to see the plc. What is the best way to fix this problem? Thanks for any suggestions.
The part number as requested above would be a help :)
One thing could possibly be that you have a node conflict or that the 5/03 isnt configured correctly for dh+ or dh485 for talking to the panelview or the panelview comms are set incorrectly!
If you post the part number of the Panelview then you could also post the channel configration you have on the 5/03 see attached pic
2711-nc13 (5meter) nc14 (10meter) connect an slc channel 0 to a panelview RS232 device and would not work on a dh485 panelview
for a dh485 panelview you would need a 1747-C10 C11 or C20 cable to connect to an slc up to 6.1 meters
The Panelview User Manual can be found here and it explains the differences and the cables http://literature.rockwellautomation.com/idc/groups/literature/documents/um/2711-um014_-en-p.pdf
Thats an RS232(DH485) device
See pic
So how far are the slc and panelview apart?
Is there anything else connected or just the slc and PV ?
If its a node problem then check these two pics
One for logix 500 and one for PB32
The nodes should be different and the comm speed should match
Thanks for the info. I will see about getting this working tomorrow. I would also like to connect a barcode scanner to the plc at the same time as the panelview. I have got a feeling that will require some more equipment. Right now I can see the barcode scanner when it is connected to the rs232 port. What do I need to have both working at same time? Thanks for your help.
-sj
To connect the barcode reader to the SLC, you will need to use CH. 0 (9-pin serial port), configured for ASCII. when that time comes, use a 1761-CBL-AS03 to connect CH. 1 (RJ-45) of the SLC, to the 6-pin Phoenix port of an AIC+: To use this cable, remove the 6-pin connector from the AIC+ and plug-in the 6-pin connector of the AS03 cable. Then connect the PanelView to the 9-pin serial port of the AIC+ with a 2711-NC13 cable. Now you can set Ch. 0 to "User" mode (ASCII) and connect your barcode reader.
hi;
I am newby with panel view, i am trying to connect the slc 5/03 to pv 550 2711-t5a16l1 servB, I connfigured the slc like 504bloke says on rslogix, nodes and all config.
I am using 1747-uic to connect to slc 5/03 by dh485 19200 bauds, then rs232 of slc 5/03 to pv 550 on df1 rs 232
my pv 5500 has to rs 232, 1.- rs 232 and 2.- d1 rs 232
could u help me ??
Miguel V.
thanks
I have been able to connect the computer to the Panelview, I cannot seem to get commication right to the PLC. Can someone help me with this?
4,187
Hi All, I have a SLC 5/04 plc that I need to communicate to - however we don't have any null modem rs232 cables on site. I am very new to Allen...
2,728
Hi guys, Working on one of my client's systems with SLC processors, earlier today she called me and said she was having comms errors, had a solid...
2,085
I recently inherited some 5/04 CPUs and a single 5/02 CPU that I need to pull the programs from. The 5/04 CPUs didn't pose any problems. I...
3,117
Hello All, I’m trying to connect some SLC 5/03 and SLC 5/04 processors to RXLinx but am unable to see the connection to the processor in the...
2,338