Convert 0-10V to +/-10V
ndzied1
Aug 2002
Chicago, Illinois
2,857
I'm trying to find an analog conditioner to convert a 0-10 V signal to a +/-10V signal and not having much luck.
Has anyone ever come across a beast like this?
I have used one from Weidmuller(wwwweidmuller.com)
Do not use relays to switch polarity unless that you have a "slow" system where you don't have to change fast from + to - voltage. I have just spent many hours of troubleshooting a problem like this.
Thanks all for the replies. The Red Lion looks like exactly what I need. The signal is to drive a proportional valve so I couldn't switch polarities w/ a relay since the valve would go wacky when I did.
Swap with a relay? NOOOOO!
A backage coming to position, or trying to hold position would NEVER satisfy position with a relay swap. Nope-nope
Rod (The CNC dude)
I should clarify how we use the relay. When the signal is proportional both ways (in, out, left, right, etc.) and the controller must go from 0 to 10 then back to 0 before it can start the other way, I have used a relay to swap polarity as the operator control moves off center to shift the other way. In this simple scenario, it works fine.
So in the past I have converted a 4-20ma signal to 0-10v using a 500ohm resistor. I am attempting to control a Johnson Controls damper motor with...
1,617
Hi, i want to convert 0-10vdc output to 4-20ma signal.
3,269
Hi! I have a Belimo SGF24 which provides a 0-10V (or selectable 2-10V) output. http://www.belimo.ch/pdf/e/2_Z_4_e5.pdf Is there a simple...
18,674
Hi, I have a MicroLogix 1100 PLC, and it has two 0-10v analog input channels. Is there a way to convert a 4-20 ma loop powered device for use with...
26,097
Have a question. Have a transducer that gives a 0-10v output. Is there a way to add a resistor so that it would appear as a 4-20ma signal?
23
54,601