CR3000 HMI ModBus TCP/IP Master has gotten erratic after increasing block size to 24 at DA70A in Protocol 1. What should a practical guide be for block assignment? Will splitting into dual Protocols help?
 
Welcome to the PLCTalk forum community !

Please clarify: is your DA70 initiating the comms to a "slave" peer, or is it answering requests from another device ?

Can you describe what you consider to be "erratic" ? Is the reply time changing, or is your client seeing a timeout ?

24 registers should be trivial to read or write with Modbus/TCP.

What kind of device is the other device ?
 
Last edited:
What i found was that I completed the 40000 mapping of Data Tags in the Communications protocol of the DA70A to match all of those entered in the CR3000 Data Tags, and the erratic display at the CR3000 has been eliminated.

I did not think the Communications protocol omission at the controller would interfere with the HMI, but I no longer can duplicate the error seen (failed button actions, numeric displays flashing blank) with the 40000 registers unassigned. Would this mapping correction really fix a problem?
 

Similar Topics

Build error occurs with TON ladder logic command. Time Input expected on block. Using Integer Tag under Control Local, and then hard number 19...
Replies
2
Views
772
Hello Everyone, I am using a raC_Opr_NetModbusTCPClient AOI module, as below,. So, I need some assistance to restrict in reducing the poling...
Replies
2
Views
91
I want to communicate my Q series PLC with Factory IO using GX works 2 software, I want to use modbus as server and the ips are as follows plc...
Replies
0
Views
68
Hi folks, I have a Controllogix in communication with a zigbee coordinator using Logix AIO for modbus tcp. This zigbee coordinator have 3 slaves...
Replies
10
Views
327
Hi, I'm setting up a modbus master on an S7-300. It seems to work in OB1 but not when I use it in OB35. Does anyone have any ideas why? Could...
Replies
10
Views
120
Back
Top Bottom