data from powerLogic pm9c by mudbus

phinix

Member
Join Date
May 2006
Location
l.a
Posts
33
hi u all,
i am trying to read data from a merlin Gerin powerlogic pm9c
i am using a laptop ,adam 4520 converter(485-322)and a modbus opc server.

i know that the device is transmitting by rs485 modbus rtu and i have configured it to work.
i know that the adam is converting 485 to 232
and i have configured it to work.
i know that the opc server should communicate with the device but it dosn't.

i get a device comunication error on the server

needless to say all baund rates and address are the same.

dear people please help!!!
 
Read pairs of registers starting at an even number

CAN ONLY READ PAIRS OF REGISTERS STARTING AT AN EVEN NUMBER
There is a trap! If You try to read one register you will get an error. If you try to read a pair of registers starting at an odd number (e.g. 1001 and 1002), you will get an error). If you try to read an odd number of registers you will get an error.
 

Similar Topics

Hi, How to get data from multiple Mitsubishi Q03UDVCPU into master PLC Q03UDVCPU through QJ71E71-100 ?
Replies
1
Views
56
When i load my client a[plication the following error is recorded in factorytalk view studio log Failed to load data server...
Replies
0
Views
53
Hello, im quite new and still learning. I would like to ask is it possible for FATEK PLC to read data value more than 16k? I'm trying to move my...
Replies
0
Views
84
Hello Everyone, I am using a raC_Opr_NetModbusTCPClient AOI module, as below,. So, I need some assistance to restrict in reducing the poling...
Replies
2
Views
152
Hi everyone, I have a 505 workshop program with PLC type of 555- 1106 and I was wondering how can I download the data documentation window as a...
Replies
8
Views
257
Back
Top Bottom