Device to convert AC input voltage to analog DC output

AB2005

Member
Join Date
Nov 2006
Location
Lahore
Posts
321
Hi;

I need to monitor and log the 3phase AC input voltage for which I need a device to convert AC input voltage (say 350 - 440V) to analog (0-10v or 4-20mA) to connect with PLC. Has anyone used such device? Please share the make and models number.
 
I agree that Power Meters need a different interface, but I have found that the prices have dropped a lot recently.
This is £169.00 with a modbus RTU output:
https://www.smartprocess.co.uk/mid-...tricity-meter-pulse-modbus-smartrail-x835-100
Or to go with a well known make, this is Siemens with a Modbus TCP output:
https://uk.rs-online.com/web/p/ener...ol_Gear_Whoop-_-Energy+Meters_Whoop-_-1809613
From these you can get Voltage, Frequency, Current, Power plus loads of other values.

If you just want one value then 4-20mA is the way to go. If you want more than one value then a bus connected device will give you a lot more data.
 

Similar Topics

I hope this makes sense. I need something that can accept the data from an Excel or csv file and can output a 4-20mA signal to represent this...
Replies
4
Views
2,282
Recently we have purchased the Rosemount 752 remote indicator to replace with new one, Capability file for that FF Device is unable to import with...
Replies
0
Views
44
Good morning everyone I’m currently working on a omron device net and have a nord drive that fell off the network. I have limit knowledge in...
Replies
3
Views
148
Anyone have a idea of what would cause a failure of all nodes (buckets) of an AB Device Net MCC upon a power cycle of the main feeder for that MCC?
Replies
17
Views
761
Hi, I'm trying to use the IO Device Library (Product Versions) which is configured to work with the 1756-EN4TR & 1756-EN2TR but my system uses...
Replies
0
Views
81
Back
Top Bottom