DH+ Panelview 1000 comm issue

swtjhny

Member
Join Date
Dec 2013
Location
IOWA
Posts
13
I have a panel view 1000 (2711 T10C8) it is communicating with a SLC 5/04 via DH+. The machine was powered down for service, when it was powered back up the screen comes up with a Error 688 No nodes found. The program is still in it. I replaced the processor thinking maybe it had a comms issue. Nothing. This screen is on a network and is the last thing on the line, everything else is working just fine. Any Ideas? Also, the configuration screen is password protected and I do not have the password.....
 
Also the comms light on the screen is blinking green, and the DH+ light on the processor is blinking as well.
 
Check and double check the wiring/termination resistors.

Go online with the processor and check the baud rate and node address. Upload the PV's program and make sure the baud rate matches the SLC and the node addresses are different.
 

Similar Topics

Last night electricians replaced the panelview and now there is no comms between the panelview and the PLC. The processor is a 1747-L541 SLC 5/04...
Replies
4
Views
931
Hi Guys... Got an issue communicating with an old (unsupported) PanelView 1000. Tried both USB converter and actual RS232 port (yes, printer...
Replies
2
Views
1,261
I have a panelview 1000 communicating with a CLX 5561 via enbt card and Pheonix switch. Began getting comm timeouts, both read and write. Tried a...
Replies
8
Views
2,249
It has two comm ports and both are labeled "RS232." From the user manual, one port is DH-485 and the other is DF1 (printer port). How can the...
Replies
36
Views
12,342
Hello, I made a change in alarm setup in factory view studio, where I changed a alarm message text. After that I made a run application and...
Replies
0
Views
183
Back
Top Bottom