PC Adapter USB has the problem that it needs 24V from the port it is attached to.
There is no 24V in the MPI/DP port on the TP177B, so the way to do it is to connect the PC adapter USB to the MPI or DP port on the S7 PLC via a Profibus connector with a PG socket. The TP177B must then be connected to the S7 PLC via a Profibus cable that goes from the port on the TP177B to the profibus connector on the S7 PLC. In this way, everything is connected together, USB adapter - S7 PLC - TP177B.
Dont know if there is any such problem with the USB-PPI cable.