ET200L-SC AI modules

userxyz

Member
Join Date
May 2002
Location
any
Posts
2,768
Hi

I have an ET200L with an SC expansion

2 analogue input cards on slots F and G.

The weird thing is, that Physically, the current inputs are wired to slot G (G1 and G3 inputs).

F = 276...279 in the hardware configuration
G = 280...283 in the hardware configuration

On slot F nothing is connected.

On PIW280 and PIW282 I get zero ?? when nothing connected I should get 32767 in think.

On PIW276 and PIW278 I get the measurements of SLOT G ?????

How is this possible ?
 
Combo said:
On PIW280 and PIW282 I get zero ?? when nothing connected I should get 32767 in think.
No, for a +/- 20mA current input, at 0 mA the value will be zero.

For the other problems, I cant help you much. I would experiment to find out how it works. Mind you that it is quite easy to get the wiring mixed up with the ET200S modules.
 
Hi

Hey,

I have found the problem,

I had the analog modules on slots G and H

and moved them to slots F and G

after downloading it's necassary to shut the power of the ET200L of and on.

Then everything is as it should

thanks
 

Similar Topics

Hi All, I have an ET200L module with part no. 133-1BL01-0XB0. I'm trying to connect it to a CPU317-2 PN/DP through profibus. The Problem that I...
Replies
10
Views
2,302
How do I do This???? We are into PLC training and intend to show CPU Redundancy on Siemens S7 412 2DP cpu's. I have following Hardware (a)...
Replies
4
Views
8,834
Does anyone have a source for old Siemens ET200L Profibus Modules? I have several that are bad and need to be replaced. I don't want to replace...
Replies
12
Views
5,658
What is the best way to show a modules LED status lights on an HMI screen? The module I'm trying to mimic is the 1756-DNB DeviceNet Scanner...
Replies
0
Views
60
We had a site where a rat gnawed through some fiber optic cables which (obviously) prevented communication to a remote rack entirely. We, and the...
Replies
3
Views
134
Back
Top Bottom